#192974 - 03/12/10 06:02 PM CU/AL Twist-on Connector
jes Offline
Member
Registered: 07/12/02
Posts: 103
Loc: CT
Is anyone aware of any other mfg that has one of these products on the market other than the Ideal Twister?
Top
2017 / 2014 NEC & Related Books and Study Guides
#192986 - 03/13/10 03:23 PM Re: CU/AL Twist-on Connector [Re: jes]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Jes:
I did a quick google search.....nothing but "purple"

_________________________
John
Top
#192987 - 03/13/10 03:38 PM Re: CU/AL Twist-on Connector [Re: HotLine1]
dougwells Offline


Member
Registered: 05/03/03
Posts: 1137
Loc: kamloops BC Canada
T&B has one under the marrette brand ,it is only listed for canada though
Top
#192989 - 03/13/10 04:43 PM Re: CU/AL Twist-on Connector [Re: dougwells]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
I donít know of any other UL listed twist-on type either, but I prefer the Alumicon connectors anyway. They allow more wire combinations and take up less room in the boxes.

Alumicon
Top
#192999 - 03/14/10 06:01 PM Re: CU/AL Twist-on Connector [Re: jes]
jes Offline
Member
Registered: 07/12/02
Posts: 103
Loc: CT
How would you all splice a #8 AL STR to a #12 CU STR in a box?
Top
#193003 - 03/14/10 09:15 PM Re: CU/AL Twist-on Connector [Re: jes]
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
The other product I use from time to time if your box do have room I used Polairs connetor block they have one for small size but again just watch out the room in the box otherwise you will get it crowed pretty bad.

Jes., If you have 4X4 box it may be ok depending on the type of recetpale you are using and size of mudring you need to get it fit in.

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#193010 - 03/15/10 04:23 PM Re: CU/AL Twist-on Connector [Re: frenchelectrican]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
#8 Al = #10 Cu in terms of ampacity; 60 degree table.

What size C/B protects this circuit?


Edited by Tesla (03/15/10 04:27 PM)
_________________________
Tesla
Top
#193315 - 03/27/10 07:04 AM Re: CU/AL Twist-on Connector [Re: Tesla]
jes Offline
Member
Registered: 07/12/02
Posts: 103
Loc: CT
Thanks for the replies.
There is no ampacity issue here, it's a 20A circuit. A number of mfgs make reducer/splicer devices that are set screw types.
Alumicon is not listed for larger than #10 AL.
Top
#193318 - 03/27/10 09:22 AM Re: CU/AL Twist-on Connector [Re: jes]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
They do make several sizes of traditional split-bolt connectors listed for copper to aluminum connection.
I don't have any specifics on them as far as minimum and maximum run conductor sizes go though.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals