Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 209 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#192828 - 03/05/10 07:40 AM changeing colors blk,red,wht. to Blk ,Green, White
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Interesting situation! Partial remodel of Existing kitchen area. Electrical only. Several Ungrounded outlets on 3 wire ungrounded #12 . New #12 circuits from Panel to ist outlets easy to get without tearing walls apart. Rest are big deal!! One wall can get new outlet boxes & romex in OK.
Other wall 2 older ungrounded outlets with 3 wire Blk,Red , Wht. Can you Change Red to Ground(Strip or tape green) tie into existing box with new romex feed thoses two. Just looking for opinions?
Yoopers

Top
2014 / 2011 NEC & Related Books and Study Guides
#192830 - 03/05/10 11:16 AM Re: changeing colors blk,red,wht. to Blk ,Green, White [Re: Yoopersup]
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
You might get away with it , but it does violate 310.12 reference to 250.119 NEC 2008.
_________________________
Alan--
If it was easy, anyone could do it.

Top
#192834 - 03/05/10 12:11 PM Re: changeing colors blk,red,wht. to Blk ,Green, White [Re: Alan Nadon]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I agree it is a technical violation but if you stripped the red wire as far back as you can see it maybe with a green wrap of tape to avoid any possible confusion, I think the safety aspect of grounded outlets outweighs the violation.
_________________________
Greg Fretwell

Top
#192842 - 03/05/10 07:39 PM Re: changeing colors blk,red,wht. to Blk ,Green, White [Re: gfretwell]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
If it a non industrial installation, I'm not sure how you could insure that only qualified individuals will service this installation, but maybe you could talk to your AHJ and see if he'll agree to let you use one of the methods for identifying the grounding conductor in multiconductor cables listed in 250.119[B].
These basically mimic what was just outlined in the post above anyway, that is, either stripping the exposed conductor bare, taping it green or coloring the exposed insulation green at every point where the wire is accssible.


Top