Interesting situation! Partial remodel of Existing kitchen area. Electrical only. Several Ungrounded outlets on 3 wire ungrounded #12 . New #12 circuits from Panel to ist outlets easy to get without tearing walls apart. Rest are big deal!! One wall can get new outlet boxes & romex in OK.
Other wall 2 older ungrounded outlets with 3 wire Blk,Red , Wht. Can you Change Red to Ground(Strip or tape green) tie into existing box with new romex feed thoses two. Just looking for opinions?
Yoopers
Top
2017 / 2014 NEC & Related Books and Study Guides
#192830 - 03/05/10 11:16 AM Re: changeing colors blk,red,wht. to Blk ,Green, White [Re: Yoopersup]
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
You might get away with it , but it does violate 310.12 reference to 250.119 NEC 2008.
_________________________
Alan--
If it was easy, anyone could do it.
Top
#192834 - 03/05/10 12:11 PM Re: changeing colors blk,red,wht. to Blk ,Green, White [Re: Alan Nadon]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I agree it is a technical violation but if you stripped the red wire as far back as you can see it maybe with a green wrap of tape to avoid any possible confusion, I think the safety aspect of grounded outlets outweighs the violation.
_________________________
Greg Fretwell
Top
#192842 - 03/05/10 07:39 PM Re: changeing colors blk,red,wht. to Blk ,Green, White [Re: gfretwell]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
If it a non industrial installation, I'm not sure how you could insure that only qualified individuals will service this installation, but maybe you could talk to your AHJ and see if he'll agree to let you use one of the methods for identifying the grounding conductor in multiconductor cables listed in 250.119[B].
These basically mimic what was just outlined in the post above anyway, that is, either stripping the exposed conductor bare, taping it green or coloring the exposed insulation green at every point where the wire is accssible.

Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkyinak), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals