The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 99 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#192698 - 02/25/10 08:30 PM AFCI dilema
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
I rewired an old house a few months ago. The owner has not moved in as of yet, since a lot of remodeling had to be done. I wired the dining room circuit on a AFCI. The breaker had been tripping when a wet vac was plugged into the circuit. I traced the problem to one outlet on a shallow wall on the back side of a fireplace. Every time I would disconnect the feed to that outlet, everything worked fine. I went up into the attic and cut the wire just before it went down into the wall to the outlet. I tried plugging something into the other outlets on the circuit then and everything was fine. I then proceeded to fish another wire down to the outlet, assuming that there was a "nick" in one of the wires. This was of course after I had checked the outlet itself. After I fished the new wire down to the outlet and hooked it up, IT STILL TRIPPED THE BREAKER!!. Since I had already spent around 3 hours checking the different outlets etc.... I proceeded to put a regular breaker on that circuit for now. The only thing I can figure is, that when I was pulling the new wire down the wall, it got scraped or something on the way down. It was a rough pull since it was right against the concrete on the back side of the fireplace. Only problem with that thought is, that I checked the wire I pulled out and didn't see any evident signs of anything wrong with it. Does anyone have another idea other than the thought that I'm crazy?? It had to work with a new wire, right??? Only thing I would know to do would be to pull another new wire down and hope it don't scrape the same thing the other two may have come in contact with. The wall was sheetrocked and paneling was put up on the lower half of the wall. Possibly a nail??
After going through with that, I just got my tools up and went home.... Thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#192701 - 02/25/10 11:20 PM Re: AFCI dilema [Re: sparkync]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
---tripping when a wet vac was plugged into the circuit.---

Before pulling the new cable,and after separating the rec. did you try the wet vac?
Did you swap out the breaker?

The AFCI- Mfg. aspect is far from perfect as of yet.

Probably a bad appliance.

Top
#192702 - 02/26/10 07:08 AM Re: AFCI dilema [Re: leland]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri
Did you eliminate the possibility of bad equipment ie plug in a radio and see if it trips?

Top
#192706 - 02/26/10 09:20 AM Re: AFCI dilema [Re: Rewire]
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2343
Loc: Vienna, Austria
And if you can megger the cable run to find any traces of bad isolation.

Top
#192710 - 02/26/10 11:23 AM Re: AFCI dilema [Re: Texas_Ranger]
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
I switched the circuit to a breaker that was working, and it still tripped. I tried the wet vac in another AFCI circuit and it worked fine. There is nothing else plugged into the circuit, since no one is living there yet. I don't have a megger. Got to be something in that wall that is snagging the wire as it goes down or something they haven't discovered yet that's in the fireplace that triggers the AFCI's smile It's a mystery UIAIW (unidentified alien in wall) :0

Top
#192711 - 02/26/10 12:51 PM Re: AFCI dilema [Re: sparkync]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Sparky:
Just a thought; you say it's a "shallow" wall. I have to ask, what kind of device box? Metal? Shallow? Any chance there's an issue within the box/terminations/device??
_________________________
John

Top
#192714 - 02/26/10 03:40 PM Re: AFCI dilema [Re: HotLine1]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Of course, I'm not there to see things first hand, but my guess would be that you could change that wire all day long and it probably won't make a bit of difference.

What brand of AFCI cb are you using?
Does it have the diagnostic LEDs on it? Those could possibly give you some indication as to what's going on.

I guess you've already checked to be sure you don't have a grounding conductor touching the neutral anywhere or a neutral from another circuit spliced together with the neutral of that circuit.

Top
#192716 - 02/26/10 05:24 PM Re: AFCI dilema [Re: KJay]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri
if all else fails cut in a metal box and use MC. But first a few diagnostic steps, remove the receptacle outlet from the box and try the circuit,remove the receptacle from the wire,disconnect the wires at the junction box. If you grt to the last step and now are holding take your meter and do an Ohm check beteen hot-neutral,hot-ground,neutral-ground this would show if any short exists.

Top
#192723 - 02/27/10 08:27 AM Re: AFCI dilema [Re: Rewire]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
I guess as a last resort you could always invoke the words of Ronald Reagan, "Mr. General Contractor... tear down this wall". laugh

Either that or just tell them the plumber said he needs to run a 1/2-inch Pex line up the wall, then for some reason they won't hesitate to remove entire sections of wallboard if deemed necessary. grin

Top
#192726 - 02/27/10 10:08 AM Re: AFCI dilema [Re: KJay]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
If you really think it is something damaging your cable, fish MC.
_________________________
Greg Fretwell

Top