#192692 - 02/25/10 01:18 PM Neutrals Combined in Outlet Box Question
rwilsond Offline
New Member
Registered: 08/24/05
Posts: 5
Loc: Rancho Santa Margarita, CA
Here's an oddity I came across. An electrician was called to a house, because of lights flickering. He came to believe there was an open in the neutral of a 2-wire branch circuit. But he was unable to locate and correct the open. So, he jumpered the neutral to the neutral of another 2-wire branch circuit, in an existing outlet box.

Which sections of the NEC did he violate?

Top
2017 / 2014 NEC & Related Books and Study Guides
#192693 - 02/25/10 02:12 PM Re: Neutrals Combined in Outlet Box Question [Re: rwilsond]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
300.3(B)? 310.4?
_________________________
Greg Fretwell
Top
#192695 - 02/25/10 03:37 PM Re: Neutrals Combined in Outlet Box Question [Re: gfretwell]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
I'd agree with you 300.3(B).
Top
#192703 - 02/26/10 07:19 AM Re: Neutrals Combined in Outlet Box Question [Re: Yoopersup]
Rewire Offline
Member
Registered: 02/23/08
Posts: 167
Loc: Missouri
210.4 (B)
Top
#192704 - 02/26/10 07:51 AM Re: Neutrals Combined in Outlet Box Question [Re: Rewire]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
210.4(B) is for ungrounded conductors not grounded conductors.
Top
#192718 - 02/26/10 05:33 PM Re: Neutrals Combined in Outlet Box Question [Re: Yoopersup]
Rewire Offline
Member
Registered: 02/23/08
Posts: 167
Loc: Missouri
Originally Posted By Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.
Top
#192719 - 02/26/10 06:33 PM Re: Neutrals Combined in Outlet Box Question [Re: Rewire]
wa2ise Offline
Member
Registered: 11/29/02
Posts: 773
Loc: Oradell NJ USA
I don't know the code, especially chapter and verse, but I think you'd have 4 bad results: a) depending on the phasing of the other circuit, if it happens to be the same phase you could get an overloaded neutral, b) Violation of that code rule saying "no paralleled wires (except for a few well restricted exceptions)", and c)the other circuit's breaker needs to be ganged with the first circuit's breaker. And you'd have current passing thru the hot wire of one cable (raceway) and returning thru a separate cable (raceway) neutral wire (because of an open on the first raceway's neutral) which I'm sure is a 4th violation and if not, still undesirable. You'd have a large loop of 60Hz magnetic activity happening, and in severe enough cases you could get magnetic inductive heating of connector and box hardware.
Top
#192720 - 02/26/10 08:31 PM Re: Neutrals Combined in Outlet Box Question [Re: wa2ise]
Rewire Offline
Member
Registered: 02/23/08
Posts: 167
Loc: Missouri
300.3 B(4) allows seperate cables as long as you comply with 300.20 B
Top
#192742 - 02/28/10 04:53 PM Re: Neutrals Combined in Outlet Box Question [Re: Rewire]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Rewire:

Originally Posted By Rewire
Originally Posted By Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


I think you should go back to the OP again! Two (2) wire branch circuits IMHO are a hot & a neutral. Therefore he now has two hots (of unknown phase) and one neutral.

Yes, a 2 pole CB (single handle) would be required, and yes, the neutral could be overloaded depending on the phasing, but that is unknown as of now.

It's a dangerous practice to do what the OP found.
_________________________
John
Top
#192744 - 02/28/10 06:02 PM Re: Neutrals Combined in Outlet Box Question [Re: HotLine1]
Rewire Offline
Member
Registered: 02/23/08
Posts: 167
Loc: Missouri
Originally Posted By HotLine1
Rewire:

Originally Posted By Rewire
Originally Posted By Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


I think you should go back to the OP again! Two (2) wire branch circuits IMHO are a hot & a neutral. Therefore he now has two hots (of unknown phase) and one neutral.

Yes, a 2 pole CB (single handle) would be required, and yes, the neutral could be overloaded depending on the phasing, but that is unknown as of now.

It's a dangerous practice to do what the OP found.
The OP needs clarity, a branch circuit by definition has 2 conductors so stating it was a 2 wire branch circuit was a bit misleading I made the assumption he was speaking of a MWBC either way a handle tie breaker would be required a simple voltage check at the box would tell you if you were on the same phase.
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (sparkyinak), 108 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals