The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 246 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#192692 - 02/25/10 01:18 PM Neutrals Combined in Outlet Box Question
rwilsond Offline
New Member

Registered: 08/24/05
Posts: 5
Loc: Rancho Santa Margarita, CA
Here's an oddity I came across. An electrician was called to a house, because of lights flickering. He came to believe there was an open in the neutral of a 2-wire branch circuit. But he was unable to locate and correct the open. So, he jumpered the neutral to the neutral of another 2-wire branch circuit, in an existing outlet box.

Which sections of the NEC did he violate?

Top
2014 / 2011 NEC & Related Books and Study Guides
#192693 - 02/25/10 02:12 PM Re: Neutrals Combined in Outlet Box Question [Re: rwilsond]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
300.3(B)? 310.4?
_________________________
Greg Fretwell

Top
#192695 - 02/25/10 03:37 PM Re: Neutrals Combined in Outlet Box Question [Re: gfretwell]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
I'd agree with you 300.3(B).

Top
#192703 - 02/26/10 07:19 AM Re: Neutrals Combined in Outlet Box Question [Re: Yoopersup]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri
210.4 (B)

Top
#192704 - 02/26/10 07:51 AM Re: Neutrals Combined in Outlet Box Question [Re: Rewire]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
210.4(B) is for ungrounded conductors not grounded conductors.

Top
#192718 - 02/26/10 05:33 PM Re: Neutrals Combined in Outlet Box Question [Re: Yoopersup]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri
Originally Posted By: Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.

Top
#192719 - 02/26/10 06:33 PM Re: Neutrals Combined in Outlet Box Question [Re: Rewire]
wa2ise Offline
Member

Registered: 11/29/02
Posts: 769
Loc: Oradell NJ USA
I don't know the code, especially chapter and verse, but I think you'd have 4 bad results: a) depending on the phasing of the other circuit, if it happens to be the same phase you could get an overloaded neutral, b) Violation of that code rule saying "no paralleled wires (except for a few well restricted exceptions)", and c)the other circuit's breaker needs to be ganged with the first circuit's breaker. And you'd have current passing thru the hot wire of one cable (raceway) and returning thru a separate cable (raceway) neutral wire (because of an open on the first raceway's neutral) which I'm sure is a 4th violation and if not, still undesirable. You'd have a large loop of 60Hz magnetic activity happening, and in severe enough cases you could get magnetic inductive heating of connector and box hardware.

Top
#192720 - 02/26/10 08:31 PM Re: Neutrals Combined in Outlet Box Question [Re: wa2ise]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri
300.3 B(4) allows seperate cables as long as you comply with 300.20 B

Top
#192742 - 02/28/10 04:53 PM Re: Neutrals Combined in Outlet Box Question [Re: Rewire]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Rewire:

Originally Posted By: Rewire
Originally Posted By: Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


I think you should go back to the OP again! Two (2) wire branch circuits IMHO are a hot & a neutral. Therefore he now has two hots (of unknown phase) and one neutral.

Yes, a 2 pole CB (single handle) would be required, and yes, the neutral could be overloaded depending on the phasing, but that is unknown as of now.

It's a dangerous practice to do what the OP found.
_________________________
John

Top
#192744 - 02/28/10 06:02 PM Re: Neutrals Combined in Outlet Box Question [Re: HotLine1]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri
Originally Posted By: HotLine1
Rewire:

Originally Posted By: Rewire
Originally Posted By: Yoopersup
210.4(B) is for ungrounded conductors not grounded conductors.
The OP said he was dealing with 2 MWBC so these 4 wires now comprise the MWBC so all 4 breakers would need to disconnect at the same time its a subtle violation.


I think you should go back to the OP again! Two (2) wire branch circuits IMHO are a hot & a neutral. Therefore he now has two hots (of unknown phase) and one neutral.

Yes, a 2 pole CB (single handle) would be required, and yes, the neutral could be overloaded depending on the phasing, but that is unknown as of now.

It's a dangerous practice to do what the OP found.
The OP needs clarity, a branch circuit by definition has 2 conductors so stating it was a 2 wire branch circuit was a bit misleading I made the assumption he was speaking of a MWBC either way a handle tie breaker would be required a simple voltage check at the box would tell you if you were on the same phase.

Top