They have a 50amp breaker and ran #6 up into a box spliced it with split bolts to #4 teck cable for the length of run then into another box spliced it again to a #6 for a drop to a machine.I know you can run #4 to #6 as long as the breaker is sized for #6 but doing it at both ends seems just plain wrong since Ive never seen this done before with ten yrs in the trade.They also used BX connectors instead teck connectors???Someone else did the work and they want me to terminate it.I will be inspected and they say i will pass but i don't think so.
opinions please
thanks
Top
Tools for Electricians:
#192666 - 02/22/10 12:58 PM Re: #6 to #4 and back to#6 [Re: frank]
Eddy Current Offline
Member
Registered: 09/26/06
Posts: 111
Loc: Ontario,Canada
I don't see a prob with the wire sizing.
Only need the teck connectors if it's outside or in a damp location. Had this come up recently where one inspector said yes, the other said no. Final answer was that if it's inside you treat it like bx. Just strip back enough of the outer casing so the connector is in contact with the metal sheath.
Top
#192667 - 02/22/10 03:22 PM Re: #6 to #4 and back to#6 [Re: Eddy Current]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
First teck connectors are required for wet locations or hazardous locations. Flex and BX connectors are approved for dry locations for teck assuming condition 1 and 2 do not exist. The biggest challenge with many of the dry connectors is that they do not tighten up to the armour thus neither a good mechanical or electrical connection.
Now #4 to #6. as long as the wire is that size for voltage drop and the OC protection is for #6 then great. Maybe the largest lugs in the supply and load would not accomodate #4 wires. I saw a job that sized all the home runs for %3 volt drop and a few receptacle runs used #6 which were spliced down to #12 for connection to breakers and receptacles. I think that job was designed by some guy that just took a harmonics and volt drop seminar. They might even recoup the added expense over a hundred years on line loss savings ;-) By the way it was an OSH (Worksafe) office in Vicoria BC.
Top
#192670 - 02/22/10 07:10 PM Re: #6 to #4 and back to#6 [Re: mikesh]
frank Offline
Member
Registered: 05/29/01
Posts: 374
Loc: windsor ontario canada
EddyCurrent,mikesh
Ok thanks for the replies

Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals