The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 18
sparky 9
gfretwell 9
sparky66wv 8
Vlado 6
Who's Online
2 registered (cableguy619, mbhydro), 230 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#192533 - 02/16/10 08:16 PM How to determine amps from Xer
Joetools Offline
New Member

Registered: 02/02/10
Posts: 9
Loc: Alberta
We have a bit of a situation, I'll do my best to explain.
Press brake is off 208/480V step up transformer. Wanting to hook up a spot welder off of the press brake. Obviously with proper disconnects as it's already a bit of a sketchy set up, being as the welder should be on it's own circuit. The spot welder is 575 volt, 15kVA. So we have another xer 480/600V for the welder. Wondering if we are going to have enough amps to run the welder? Both machines will never be on at the same time.

Top
2014 / 2011 NEC & Related Books and Study Guides
#192535 - 02/16/10 08:28 PM Re: How to determine amps from Xer [Re: Joetools]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
what type of welder that run from 480X600 transfomer due there are few diffrent type of welders that will affect the rating on the whole thing.

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#192542 - 02/16/10 09:06 PM Re: How to determine amps from Xer [Re: frenchelectrican]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri
what are you feeding the 208/480 transformer with?

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals