#19243 - 12/22/02 07:18 AM What classification is this location?
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
I am working in a warehouse/production warehouse where the company makes wooden garage doors. There are many table saws,dust collectors,routers,sanders...Anotherwords it is a huge wood working shop.
What class is this location classified?
Class1,2 or 3?
_________________________
Thanks
Edward
Top
Work Gear for Electricians and the Trades
#19244 - 12/22/02 05:33 PM Re: What classification is this location?
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
prob. class II

(1999) 500-8 Class II Locations: 'are those that are hazardous because of the presence of combustible dust....see 500-8(a) & (b) for Div. 1 & 2 conditions.... Art. 502 then gets into the wiring methods for each division.
Top
#19245 - 12/23/02 10:34 AM Re: What classification is this location?
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
Normal saw dust is not enough to justfy a Class II environment.

We have a door manufacturer, down the road, and nothing in the production area is "explosion-proof" rated.

However, we let the local fire department determine all of our classifications.
Top
#19246 - 12/23/02 06:24 PM Re: What classification is this location?
Mike Wescoatt Offline
Member
Registered: 06/17/01
Posts: 161
Loc: Cedar City, Utah
In our wood and metal shops we don't have any special requirements set by the Fire Marshall, but we take it an extra step and make everything NEMA 3 or better; no NEMA 1 enclosures. We do have dust collection and fume extraction, though.
_________________________
Mike Wescoatt
Top
#19247 - 12/24/02 06:05 PM Re: What classification is this location?
nesparky Offline
Member
Registered: 06/21/01
Posts: 642
Loc: omaha,ne
This depends on several factors Number of air changes/minute, is the dust collected and routed away from electrical equipment, layout of the equipment, etc.
This is why we ask the fire marshal to make the determination. They usually can get the designers to do all the engineering necessary to properly make the call. The fire marshal's office usually has a big enough hammer to get this done- if they care to.
_________________________
ed
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals