#192138 - 01/28/10 07:18 PM Watch them old sockets!! (NZ)
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
I was in a house yesterday, doing some repairs to a lighting circuit, when the home owner asked me to check the wiring, etc, for her.
I started off checking the socket-outlet circuits with an Earth Loop tester, all seemed to be OK, until I tested a socket in the laundry, that the dryer was plugged into.

It failed miserably, in fact, as far as the test result went, it said there was no Earth connection at all.
I isolated the circuit and took the socket off the wires in the mounting block and had a look at the socket contacts, here is what I found:



{Bear in mind, that I'd already removed the actual face of the socket, before I took this picture.}

What we have here, is a socket, of about 1960's era manufacture, it is known as a PDL Cat No. 60.
If you see the other two contacts for the phase and neutral pins of the plug-top, that is the way they are supposed to look, with the two strips almost touching.
If you now look at the Earth contact to the front of the picture, it's splayed wide open. whistle

There are probably hundreds, if not thousands of these sockets in houses around New Zealand, with splayed Earth contacts like this one, the thing that worries me the most is the fact that a lot of people don't even know they are in this condition.

I would never have known unless I'd done an Earth loop test either.
Just something for you NZ sparkies/inspectors to be aware of.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
Tools for Electricians:
#192144 - 01/29/10 12:12 PM Re: Watch them old sockets!! (NZ) [Re: Trumpy]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Trumpy:
Although I probably will never see one of these, I have to ask..
Is that a mfg defect, or is the contact 'bent' from usage?
_________________________
John

Top
#192145 - 01/29/10 12:29 PM Re: Watch them old sockets!! (NZ) [Re: HotLine1]
uksparx Offline
Member

Registered: 04/25/05
Posts: 44
Loc: Egremont,Cumbria,UK
Trumpy - I have found a very similar thing happens here in the UK. Particularly with some sockets from the 1970s made by Volex. It seems the constant in-and-out of the plug over time makes the contacts lose their spring tension. We also probably have thousands still in use that no one has discovered yet.

Top
#192157 - 01/30/10 02:57 AM Re: Watch them old sockets!! (NZ) [Re: HotLine1]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Originally Posted By: HotLine1

Is that a mfg defect, or is the contact 'bent' from usage?

John,
It's caused by normal wear and tear during use over that time-span.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#192176 - 01/30/10 02:33 PM Re: Watch them old sockets!! (NZ) [Re: Trumpy]
Alan Belson Offline
Member

Registered: 03/23/05
Posts: 1801
Loc: Mayenne N. France
From the pic, it looks like the earth pin is longer than the other two, so as it makes contact first. That could impose a side load on the earth contacts before the plug gets aligned properly. As such, as you say, this fault will exist on a lot of other sockets. It looks solidly built, with good size brass screws and copper sections. Is there any function to the strange 'overlap' feature at the back of the pic?
And did you cut yourself taking it apart, Mike? smirk
_________________________
Wood work but can't!

Top
#192178 - 01/30/10 06:25 PM Re: Watch them old sockets!! (NZ) [Re: Alan Belson]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Alan,
The earth pin on an AS/NZ plug is always longer than the other two pins, so that it "makes" first and "breaks" last.

The overlap at the back is for the switch mechanism of the socket, there is a plastic toggle that sits on top of the strip of brass, it is held in place by the front plate.

Them reddish spots are actually part of the "plastic" moulding, this was from a time when plastic was first being used to make electrical accessories, as opposed to the bakelite that was used in earlier fittings.
This plastic isn't unlike bakelite, as in, if you aren't careful and drop a socket like this on a bare concrete floor, you can almost put money on the fact of it breaking into at least 3 pieces. crazy


Edited by Trumpy (01/30/10 06:26 PM)
Edit Reason: Typo
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#192190 - 01/31/10 03:47 PM Re: Watch them old sockets!! (NZ) [Re: Trumpy]
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2343
Loc: Vienna, Austria
Looks like they used random color granulate or even recycled plastics. There were some switch boxes here where they used odd coloured leftovers all thrown together because they were cheaper.

Top
#192378 - 02/11/10 04:31 AM Re: Watch them old sockets!! (NZ) [Re: Texas_Ranger]
RODALCO Offline
Member

Registered: 12/08/05
Posts: 863
Loc: Titirangi, Akld, New Zealand
I have struck a few of them over the years, The dreaded spreaded earth contacts of the PDL 60 series.

I still have quite a few of them in my house, must do a loop impedance test on them.

It always seem to be the earths having the problems (longer pin on plug ) or poor beryllium copper which looses it's tensile strength.

Never seen spreaded phase or neutral contacts.

An other fault of these plugs is that they fill up with dust over the years.
_________________________
The product of rotation, excitation and flux produces electricty.

Top
#192402 - 02/11/10 07:00 PM Re: Watch them old sockets!! (NZ) [Re: RODALCO]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Originally Posted By: RODALCO


Never seen spreaded phase or neutral contacts.

It is rather strange how that's true, Ray.
Mind you with mandatory earth-loop testing here, hopefully most of these sockets will be weeded out in due course.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#192522 - 02/16/10 06:15 PM Re: Watch them old sockets!! (NZ) [Re: Trumpy]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Trumpy:

I have to ask, is the earth contact a single piece with spring tension, or is it two pieces, like two "L"'s that are held in place by a stud under that nice termination lug?

Or, is your earth pin much wider than the other pins on the male cap?
_________________________