#191863 - 01/16/10 01:23 PM 15 amp circuit stumper
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
This one has me stumped.
Here the situation.

15 amp circuit trips when heater plugged into it. Nothing else on circuit.
Ammeter reads 12.5 amps at breaker.
Same heater runs fine on an other circuit drawing same 12.5 amps

OK, bad breaker you say. Swapped breaker with one beside it in panel. Still trips.
Breaker is not hot. Takes about 5 minutes to trip.
Remove breaker and inspected bus. Looks perfect as does breaker contact.

What to check next?

Breaker panel is only about 15 years old FPE. I installed it and I also installed the circuit so I know where the cable runs exactly.

Don't bitch about FPE panel. We still install them new here in Canada. Very popular brand.
Top
Work Gear for Electricians and the Trades
#191864 - 01/16/10 02:19 PM Re: 15 amp circuit stumper [Re: jdevlin]
electure Offline


Member
Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
"Swapped breaker with one beside it in panel. Still trips."

My suggestion is to replace the breaker with a brand new one, instead of a used one that may or may not have the same problems.

Top
#191865 - 01/16/10 04:21 PM Re: 15 amp circuit stumper [Re: jdevlin]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1310
Loc: Alaska
By change the breaker that is tripping a gfci breaker? Another thing you can do is instead of clamping the load wire, clamp the main line. Does your meter have a max hold feature that changes only when the voltage increases?
_________________________
"Live Awesome!" - Kevin Carosa
Top
#191866 - 01/16/10 05:14 PM Re: 15 amp circuit stumper [Re: sparkyinak]
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
Breaker is not GFCI or AFCI. I was clamped right at the breaker. I did use the hold feature and it did not spike high. The high max was 12.55 amps.

Do you think it is possible that more than one breaker could be tripping at the low value?

I guess a new breaker should be next try? Anything else that could possibly cause something like this?
Top
#191867 - 01/16/10 05:22 PM Re: 15 amp circuit stumper [Re: jdevlin]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Swap with the breaker you know it works on
_________________________
Greg Fretwell
Top
#191872 - 01/16/10 10:08 PM Re: 15 amp circuit stumper [Re: gfretwell]
leland Offline
Member
Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Bad cable? Takes 5 minutes to trip,maybe that long to heat up the conductors and find a fault in the insulation.
Top
#191875 - 01/16/10 11:03 PM Re: 15 amp circuit stumper [Re: leland]
twh Offline
Member
Registered: 03/11/04
Posts: 899
Loc: Regina, Sask.
I'm not surprised that two breakers, possibly from the same batch, both trip at the same value, and no one thinks that FPE has mastered the making of breakers.
Top
#191876 - 01/16/10 11:09 PM Re: 15 amp circuit stumper [Re: twh]
IanR Offline
Member
Registered: 12/06/04
Posts: 326
Loc: Palm Bay FL USA
Hmm, an FPE that trips early? I thought they usually had the opposite problem wink
Top
#191878 - 01/16/10 11:41 PM Re: 15 amp circuit stumper [Re: IanR]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8560
Loc: SI,New Zealand
Did you open and check the receptacle you originally had the heater plugged into?
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#191887 - 01/17/10 08:49 AM Re: 15 amp circuit stumper [Re: Trumpy]
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
The receptacle has been opened. What type of problem in a receptacle could make a breaker trip at 12.5 amps?

Trying to understand what other than the breaker could be the problem now that I have been think more about this.
Top
Page 1 of 4 1 2 3 4 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 89 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals