The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
09/27/16 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 49 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 4 1 2 3 4 >
Topic Options
Rate This Topic
#191863 - 01/16/10 01:23 PM 15 amp circuit stumper
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
This one has me stumped.
Here the situation.

15 amp circuit trips when heater plugged into it. Nothing else on circuit.
Ammeter reads 12.5 amps at breaker.
Same heater runs fine on an other circuit drawing same 12.5 amps

OK, bad breaker you say. Swapped breaker with one beside it in panel. Still trips.
Breaker is not hot. Takes about 5 minutes to trip.
Remove breaker and inspected bus. Looks perfect as does breaker contact.

What to check next?

Breaker panel is only about 15 years old FPE. I installed it and I also installed the circuit so I know where the cable runs exactly.

Don't bitch about FPE panel. We still install them new here in Canada. Very popular brand.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#191864 - 01/16/10 02:19 PM Re: 15 amp circuit stumper [Re: jdevlin]
electure Offline

Member

Registered: 12/24/00
Posts: 4225
Loc: Fullerton, CA USA
"Swapped breaker with one beside it in panel. Still trips."

My suggestion is to replace the breaker with a brand new one, instead of a used one that may or may not have the same problems.


Top
#191865 - 01/16/10 04:21 PM Re: 15 amp circuit stumper [Re: jdevlin]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
By change the breaker that is tripping a gfci breaker? Another thing you can do is instead of clamping the load wire, clamp the main line. Does your meter have a max hold feature that changes only when the voltage increases?
_________________________
"Live Awesome!" - Kevin Carosa

Top
#191866 - 01/16/10 05:14 PM Re: 15 amp circuit stumper [Re: sparkyinak]
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
Breaker is not GFCI or AFCI. I was clamped right at the breaker. I did use the hold feature and it did not spike high. The high max was 12.55 amps.

Do you think it is possible that more than one breaker could be tripping at the low value?

I guess a new breaker should be next try? Anything else that could possibly cause something like this?

Top
#191867 - 01/16/10 05:22 PM Re: 15 amp circuit stumper [Re: jdevlin]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Swap with the breaker you know it works on
_________________________
Greg Fretwell

Top
#191872 - 01/16/10 10:08 PM Re: 15 amp circuit stumper [Re: gfretwell]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Bad cable? Takes 5 minutes to trip,maybe that long to heat up the conductors and find a fault in the insulation.

Top
#191875 - 01/16/10 11:03 PM Re: 15 amp circuit stumper [Re: leland]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
I'm not surprised that two breakers, possibly from the same batch, both trip at the same value, and no one thinks that FPE has mastered the making of breakers.

Top
#191876 - 01/16/10 11:09 PM Re: 15 amp circuit stumper [Re: twh]
IanR Offline
Member

Registered: 12/06/04
Posts: 326
Loc: Palm Bay FL USA
Hmm, an FPE that trips early? I thought they usually had the opposite problem wink

Top
#191878 - 01/16/10 11:41 PM Re: 15 amp circuit stumper [Re: IanR]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8530
Loc: SI,New Zealand
Did you open and check the receptacle you originally had the heater plugged into?
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#191887 - 01/17/10 08:49 AM Re: 15 amp circuit stumper [Re: Trumpy]
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
The receptacle has been opened. What type of problem in a receptacle could make a breaker trip at 12.5 amps?

Trying to understand what other than the breaker could be the problem now that I have been think more about this.

Top