#191846 - 01/15/10 08:53 PM Wiring for office cubicles
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
Is there a rule of thumb for the amount of circuits to be ran in an office setting with approx. 10 cubicles. Each would have a computer, monitor, and printer. I'm going to figure 1 amp for a single computer, and 1 amp for a single monitor. Are the desktop printers in the range of 2 amps? The computers, I would think should be figured with continuous duty, 125% added in. Thanks
Top
Work Gear for Electricians and the Trades
#191849 - 01/15/10 10:06 PM Re: Wiring for office cubicles [Re: SJT]
noderaser Offline
Member
Registered: 03/01/07
Posts: 404
Loc: Portland, Oregon, United State...
CRT or LCD monitor? Inkjet or laser printer? Computers can vary a lot, depending on how much kludge is in the box... A standard computer is probably around 100W or less, but professional workstations with multiple processors and hard drives can be more.
_________________________
http://www.hsiprodsvcs.com/
Top
#191850 - 01/15/10 10:34 PM Re: Wiring for office cubicles [Re: SJT]
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
One thing I'd ask is if the people will be allowed to have portable heaters. Some people can't live without them. There might be a copy machine that will need its own circuit too.

Bill
Top
#191856 - 01/16/10 11:12 AM Re: Wiring for office cubicles [Re: Bill Addiss]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
First & foremost IMHO, the following info should be available to the EC. Are cubicles 'new' or 'pre-owned'; equipped with factory' wiring harnesses? Or is the EC doing it from scratch?

Factory units must be wired to mfg instructions.

Otherwise, if it's a 'scratch' job, & the budget range of the job, 5 amps per ststion, 3 stations per 20 amp (derated); 4x20amp circuits would be my minimum.
Now...electric heat? 1 circuit each station! Toaster ovens? Don't laugh, I've been there!

_________________________
John
Top
#191857 - 01/16/10 11:16 AM Re: Wiring for office cubicles [Re: Bill Addiss]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I think you better bump that 100w up a bit. The PC that I am typing on now is pulling a tad over 180w just sitting here and when the CPU really cranks up (IE editing a video file) it goes over 200. That is a 2.8gz single core computer, 15" LCD monitor, a switch and a router. Ink Jet printer idle.
Just for Gee whiz info the Kilawatt device says I used 459 KWH in 2516 hours.

That translates to at least 2 amps

If they are going to have a laser printer, add 10 amps.

What is the wiring method? If they have an under the floor raceway/duct system you have a chance to upgrade. Nobody ever got in long term trouble putting too much power into an office but sometimes it takes a few years to prove them right. Going for the minimum usually bites you in the butt fairly soon.
_________________________
Greg Fretwell
Top
#191859 - 01/16/10 11:47 AM Re: Wiring for office cubicles [Re: HotLine1]
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Originally Posted By HotLine1
Now...electric heat? 1 circuit each station! Toaster ovens? Don't laugh, I've been there!
Don't forget Coffee maker(s)

smile
Bill
Top
#191861 - 01/16/10 12:14 PM Re: Wiring for office cubicles [Re: Bill Addiss]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
The last pre-fab cubicles were arranged with three 20-amp circuits shared over five cubicles, if that's any help.
Top
#191871 - 01/16/10 09:07 PM Re: Wiring for office cubicles [Re: renosteinke]
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
The cubicles were pre-wired with factory assemblies. They may be the 8 pin type. It was set up with 2 circuits, and they want a third circuit. Looks like the in house Electricians will have to open the existing outlets to find where the circuits originate from.
Good Weekend
Top
#191873 - 01/16/10 10:18 PM Re: Wiring for office cubicles [Re: SJT]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Rule of thumb for general open office is 4 cubicals. If you suspect extra electrical loads like coffee makers, boot dryers and such, 3 per circuit.


Edited by sparkyinak (01/16/10 10:18 PM)
_________________________
"Live Awesome!" - Kevin Carosa
Top
#191874 - 01/16/10 10:56 PM Re: Wiring for office cubicles [Re: gfretwell]
noderaser Offline
Member
Registered: 03/01/07
Posts: 404
Loc: Portland, Oregon, United State...
Originally Posted By gfretwell
I think you better bump that 100w up a bit. The PC that I am typing on now is pulling a tad over 180w just sitting here and when the CPU really cranks up (IE editing a video file) it goes over 200. That is a 2.8gz single core computer, 15" LCD monitor, a switch and a router.


Ok, let's say 200W... My two computers (one Mac Mini and one AthlonX2) and CRT draw 320W. Figure 60W on the CRT, 40-60W for the Mini and 200-220W on the Athlon. Could do more comprehensive tests, but that would require a shutdown.


Edited by noderaser (01/16/10 11:01 PM)
_________________________
http://www.hsiprodsvcs.com/
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 05/03/03
Posts: 1137
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals