The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 196 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#19168 - 12/21/02 04:18 AM Transformer Fire??
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Transformer fire

 Quote:
Any idea why a 15 year old 75 kva single phase oil immersed pole mounted distribution transformer would suddenly blow a hole through the bottom of the tank, pop its lid and spew flaming oil out onto the surrounding area? Examination after the fact indicated a turn to turn short in the secondary windings. But why?

Thanks.

Geoffrey




[This message has been edited by Joe Tedesco (edited 12-27-2002).]
_________________________
Joe Tedesco, NEC Consultant

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#19169 - 12/21/02 06:11 PM Re: Transformer Fire??
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
The winding fault and resulting catastrophic failure is from conductor insulation failure. The insulation failure could be from a continuous overvoltage condition, overload or manufacturer assembly failure. Most likely an overload. This transformer was probably serving 3-5 residences and as typical for a utility transformer, it is easier for them to replace it after failure, as opposed to monitor loads and apply it correctly to the loads or application.
Consider that the full load current of the transformer secondary is 312.5A @ 240V, and many new utility services are 240V and 200A plus.
Interesting question from an attorney.


[This message has been edited by Ron (edited 12-21-2002).]
_________________________
Ron

Top
#19170 - 12/26/02 09:34 PM Re: Transformer Fire??
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
It may be wise to avoid NEC 450 numbers with respect to a utility-owned transformer. Design and application of these devices is based on significantly different standards.

Litigation based on applying the NEC to poletop oil-insulated transformers would likely be unsuccessful.

Top
#19171 - 12/27/02 09:12 AM Re: Transformer Fire??
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
I never realized that this question was from a lawyer! I should have been more careful. In the meantime the lawyer should not have asked a legal question of me and should have hired a consultant!

Bill please lock this message out.