#191608 - 01/04/10 06:30 PM lights blinking
mike collins Offline
Member
Registered: 05/04/05
Posts: 15
Loc: Quincy
I have a residential house wired in rx single phase, which has a intermitten blicking of lights, they do not go off they just dime.
Things I have done or checked.
Power co replaced neutral splice at weatherhead.
Tightened every connection in panel.
Checked ground wire at street side of water meter.
Pulled meter and check connections, which were fine.

The dimming seems to happen on every circuit, not just one.

My next step is to call power co. again to check meter,and 230volt lines.
Any ideas out there?
Mike
_________________________
dukes
Top
Work Gear for Electricians and the Trades
#191609 - 01/04/10 06:48 PM Re: lights blinking [Re: mike collins]
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
Do any lights get brighter at the same time as other lights get dimmer? The neutral at the power company's transformer could be bad, and no amount of solid ground connections in the customer's house will help that. The power company would have to fix that.

Do the lights in neighbors' house (fed by the same transformer) also dim, and at the same time? In addition to the above possible bad neutral at the power company transformer, could be a bad connection on the primary side of the power company transformer, which obviously you don't want to touch!
Top
#191610 - 01/04/10 07:32 PM Re: lights blinking [Re: wa2ise]
mike collins Offline
Member
Registered: 05/04/05
Posts: 15
Loc: Quincy
The house next door which is off the same trans. does not have this problem.
I wonder if the meter might be defective.
Thanks for your response
_________________________
dukes
Top
#191612 - 01/04/10 08:56 PM Re: lights blinking [Re: mike collins]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
Look for something starting, or trying to start. It might be a motor in an old fridge or freezer. The weather is cold, so it could even be a large electric heater or furnace blower.
Top
#191615 - 01/05/10 12:36 AM Re: lights blinking [Re: twh]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Ever thought about an under-sized service?
Also, have you listened to the panel to see if there is a bad phase busbar in there at all?
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#191619 - 01/05/10 05:49 AM Re: lights blinking [Re: twh]
mike collins Offline
Member
Registered: 05/04/05
Posts: 15
Loc: Quincy
Thanks I will check
_________________________
dukes
Top
#191621 - 01/05/10 06:27 AM Re: lights blinking [Re: mike collins]
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
I would have POCO check all connections at street. I had a problem and they fixed the connection at the weatherhead and were about to leave and insisted they take a look at the street side connection and sure enough there was the problem. Old street in Weston MA, and the connections were corroded at the transformer end.

shortcircuit
Top
#191622 - 01/05/10 07:52 AM Re: lights blinking [Re: shortcircuit]
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
Did the POCO check only the neutral connections? They should check all the connections
Top
#191623 - 01/05/10 10:43 AM Re: lights blinking [Re: mike collins]
CDS Offline
Member
Registered: 06/28/06
Posts: 34
Loc: Nicholson Ga
Had this problem before , and went round and round with power company . Turned out that they dont check connections behind the meter , I had to meet them there , they pulled the meter and I tightened loose neutral in meter base .


Sorry ,I just read you already did that . A logger at panel would tell you if it is inside or outside .


Edited by CDS (01/05/10 10:45 AM)
Top
#191624 - 01/05/10 10:46 AM Re: lights blinking [Re: CDS]
CDS Offline
Member
Registered: 06/28/06
Posts: 34
Loc: Nicholson Ga
One more thought , if it is SE cable from meter to panel , check for corrosion going through concrete block , etc .
Top
Page 1 of 4 1 2 3 4 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 20 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals