#19107 - 12/20/02 12:07 PM GFI breaker vs GFI outlet  
BurnOut  Offline
Member
Joined: Dec 2002
Posts: 10
Long Island, NY
who would win?

If there is a gfi breaker for outdoor outlets, but the outlets are regular outlets in an outdoor box, is that safe?

Or would it be a better to replace the outlets with gfi outlets, even though the power feeding this outdoor wiring is a GFI breaker?


Work Gear for Electricians and the Trades

#19108 - 12/20/02 12:16 PM Re: GFI breaker vs GFI outlet  
spyder  Offline
Member
Joined: Oct 2002
Posts: 210
Massachusetts
If the entire branch circuit is GFCI protected, then there is no need to install GFCI recps.


#19109 - 12/20/02 12:19 PM Re: GFI breaker vs GFI outlet  
BurnOut  Offline
Member
Joined: Dec 2002
Posts: 10
Long Island, NY
thanks for the quick reply spyder [Linked Image]


#19110 - 12/20/02 02:18 PM Re: GFI breaker vs GFI outlet  
SvenNYC  Offline
Member
Joined: Aug 2002
Posts: 1,691
New York City
I'm curious. What can happen if you put a GFCI recptacle on a circuit already protected by a GFCI breaker?

Will it cause confusion if one of them trips, will both trip or neither, or will the outlet trip first? [Linked Image]


#19111 - 12/20/02 04:38 PM Re: GFI breaker vs GFI outlet  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,799
Brick, NJ USA
Sven:
Dependent on the "sensitivity" of each device, and if they are wired properly..one will trip.
I see GFI receptacles that are inproperly installed, and I put the tester in, crank in 4-5- milliamps, and the "downstream" device trips. Then it's red sticker time.
John


John

#19112 - 12/20/02 04:43 PM Re: GFI breaker vs GFI outlet  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
At least one should trip, but if the tester is connected to the receptacle, they may both trip. It would depend on the speed of the trips and the actual trip point.
don


Don(resqcapt19)

#19113 - 12/20/02 07:00 PM Re: GFI breaker vs GFI outlet  
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
Heh...this scenario reminds me of the odd time when there is a short in a 15amp line in a house, sometimes the short by-passes the single 15A breaker and trips the 100A main.



Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,137
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.002s) Memory: 0.7817 MB (Peak: 0.9329 MB) Zlib enabled. Server Time: 2017-03-26 01:33:53 UTC