#19098 - 12/19/02 06:15 PM Short Circuit
Superduty Offline
Junior Member
Registered: 12/19/02
Posts: 3
Loc: Denver, CO USA
We have a 20amp-120v ballasted lighting circuit that opens after 48 hrs of non continuous load. It operates 3 - 3.6 amp ballast's that are all in their range according to Advance, and they run through a 25 amp photocell. All fourescent sign lights are working & we have changed the breaker & phtotcell & one leaking ballast.
Thanks, Mike
Top
Work Gear for Electricians and the Trades
#19099 - 12/19/02 06:51 PM Re: Short Circuit
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Have you put an amprobe on the circuit to verify that 10.8A is in fact all you are drawing? Maybe there is something else on the line you don’t know about.
Top
#19100 - 12/19/02 08:12 PM Re: Short Circuit
Superduty Offline
Junior Member
Registered: 12/19/02
Posts: 3
Loc: Denver, CO USA
Nick,

Thanks for your input, we used a clamp on amprpobe and got just under 11amps total.
Top
#19101 - 12/20/02 04:51 AM Re: Short Circuit
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
You may have to rent a recording ampmeter and check the loads. This way you can tell when the circuit peaks and trips the breaker which may give you some clues as to what is happening. I think GE Supply rents this kind of equipment.
Top
#19102 - 12/20/02 10:17 AM Re: Short Circuit
gregoryf Offline
Member
Registered: 08/23/02
Posts: 19
Loc: Ketchikan AK USA
My bet is one of the other 2 ballasts is going out. I would replace the other 2 now. I am assuming you have already replaced all 3 lamps.....
Top
#19103 - 12/20/02 05:23 PM Re: Short Circuit
Superduty Offline
Junior Member
Registered: 12/19/02
Posts: 3
Loc: Denver, CO USA
Thanks for your input.

I checked to make sure all that was on this line was the 3 ballasts. I isolated them and each draws 3.6 amps each.
The load has been continuous for 36 hrs now and the 20amp breaker is warm to the touch. 12 gauge wire to the panel.
Should we separate these signs and give them each their own circuit?
1 has 4- 10 foot HO lamps= 1 ballast.
1 has 10- 6 foot HO lamps= 1 ballast per 5.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals