The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#19098 - 12/19/02 06:15 PM Short Circuit
Superduty Offline
Junior Member

Registered: 12/19/02
Posts: 3
Loc: Denver, CO USA
We have a 20amp-120v ballasted lighting circuit that opens after 48 hrs of non continuous load. It operates 3 - 3.6 amp ballast's that are all in their range according to Advance, and they run through a 25 amp photocell. All fourescent sign lights are working & we have changed the breaker & phtotcell & one leaking ballast.
Thanks, Mike

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#19099 - 12/19/02 06:51 PM Re: Short Circuit
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
Have you put an amprobe on the circuit to verify that 10.8A is in fact all you are drawing? Maybe there is something else on the line you don’t know about.

Top
#19100 - 12/19/02 08:12 PM Re: Short Circuit
Superduty Offline
Junior Member

Registered: 12/19/02
Posts: 3
Loc: Denver, CO USA
Nick,

Thanks for your input, we used a clamp on amprpobe and got just under 11amps total.

Top
#19101 - 12/20/02 04:51 AM Re: Short Circuit
WARREN1 Offline
Member

Registered: 05/09/01
Posts: 184
Loc: Greenville, SC, USA
You may have to rent a recording ampmeter and check the loads. This way you can tell when the circuit peaks and trips the breaker which may give you some clues as to what is happening. I think GE Supply rents this kind of equipment.

Top
#19102 - 12/20/02 10:17 AM Re: Short Circuit
gregoryf Offline
Member

Registered: 08/23/02
Posts: 19
Loc: Ketchikan AK USA
My bet is one of the other 2 ballasts is going out. I would replace the other 2 now. I am assuming you have already replaced all 3 lamps.....

Top
#19103 - 12/20/02 05:23 PM Re: Short Circuit
Superduty Offline
Junior Member

Registered: 12/19/02
Posts: 3
Loc: Denver, CO USA
Thanks for your input.

I checked to make sure all that was on this line was the 3 ballasts. I isolated them and each draws 3.6 amps each.
The load has been continuous for 36 hrs now and the 20amp breaker is warm to the touch. 12 gauge wire to the panel.
Should we separate these signs and give them each their own circuit?
1 has 4- 10 foot HO lamps= 1 ballast.
1 has 10- 6 foot HO lamps= 1 ballast per 5.