#190712 - 12/01/09 10:12 AM 225.32 disco or not
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
I am a little confused about this articles intention. I thought i had to put a disconnect ahead of my 200 amp panel 25 feet inside this house(fed from remote meter, 100 feet away)I called my AHJ and told him I cancelled my inspection, so I can put a 200 amp disco ahead of my panel. He told me I didn't need a disconnect ahead of my panel. He is my AHJ, so I didn't put one in. What is the intention of this code? does it apply to residential? Remote meter, feeds shop, house and well house more than one structure.

Thanks,
H2O
Top
2017 / 2014 NEC & Related Books and Study Guides
#190713 - 12/01/09 10:49 AM Re: 225.32 disco or not [Re: watersparkfalls]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
H2O:
Are we talking a feeder or service conductors? Do you have OCP at the meter location?

If you have the '08 Handbook, read the commentary following this article for a good explanation.

_________________________
John
Top
#190718 - 12/01/09 12:44 PM Re: 225.32 disco or not [Re: HotLine1]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Well, there's an NEC section that sure uses a lot of words to say ... nothing!

H2O, it looks like the AHJ has given you a break. I also think the NEC is the wrong code to look at. While I'm not entirely sure of the source(fire code? building code? somewhere else?), the principle that every structure have some means of outside disconnect accessible to fire crews is pretty well established.

If the disconnect is to be at the service, you might be able to simply post a sign on the building advising of it's location.

Oddly enough, the section you cite is not the place where the main exception to this principle happens: farms. Farms will often have disconnects clusteres at the service, which is often a pole in the middle of a group of buildings.

The disco doesn't need to be a 'disconnect switch' as such; a main breaker with a shunt-trip would allow the use of a simple snip switch as the disconnecting means.
Top
#190721 - 12/01/09 03:13 PM Re: 225.32 disco or not [Re: renosteinke]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
I take it he means theres a Pole 100 feet from the Panel , Theres a underground run from the meter on that pole to a disconnect 25 feet inside the house. NO protection till the Service rated switch 25 feet inside. IF so thats a Clear violation 230.70 (A).
I'd say a disconnect has to be either at the pole . (Then conductors are a feeder and another disconnect is Still required at the house (225.31)
Or no disconnect at the pole BUT one would required at the house per 230.70 (A).
Top
#190724 - 12/01/09 06:52 PM Re: 225.32 disco or not [Re: Yoopersup]
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
I should reword my post from remote meter to - remote service.
I have established the service on well house and the feeders to the house are protected by a main 200 amp breaker, then go underground 100 feet into house via LB and Jbox to 200 amp main breaker panel 25 feet away from LB.
I am still thinking/wondering(although AHJ approved)that where conductors enter house need disconnect because, they don't terminate at closet point of entry. They are feeders is this why they don't need a disco at house? Since they already have means of disconnecting at main breaker?
Thanks again,
H2O
Top
#190728 - 12/01/09 09:50 PM Re: 225.32 disco or not [Re: watersparkfalls]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
Originally Posted By watersparkfalls
I should reword my post from remote meter to - remote service.
I have established the service on well house and the feeders to the house are protected by a main 200 amp breaker, then go underground 100 feet into house via LB and Jbox to 200 amp main breaker panel 25 feet away from LB.
I am still thinking/wondering(although AHJ approved)that where conductors enter house need disconnect because, they don't terminate at closet point of entry. They are feeders is this why they don't need a disco at house? Since they already have means of disconnecting at main breaker?
Thanks again,
H2O


Hard to say, but IMO, since this is a feeder that originates from outside the building, you would need a service rated disconnecting means for this separate building or structure per 225.31 and 225.32, unless 225.32, Exceptions 1 thru 4 applied, which doesn't sound like they would in this case.
The disconnect would need to be readily accessible and located either outside the building or inside nearest to the point of entrance of the conductors, similar to the requirements for a service disconnecting means in 230.70.

If there is a main breaker panel installed in the house, maybe the inspector feels the main CB in the panel is adequate. If so... cheers
Top
#190747 - 12/02/09 08:38 PM Re: 225.32 disco or not [Re: KJay]
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
I agree Reno... I just have to accept that it's signed off.
And if another inspector comes to final it and tries to write a correction for it, I will protest it...especially since I was told by AHJ that I didn't need it, when I was going to put one in. I'll never pass an inspection(first go around) again by that AHJ I'm sure.
Thanks guys,
H2O
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals