The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 282 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#190491 - 11/20/09 05:07 PM Confused about outside outlet requirements
Grover Offline
Member

Registered: 01/19/05
Posts: 110
Loc: Sebago, ME, USA
Customer has added a mother-in-law cottage adjacent to his primary residence. "Cottage" is above a 2 car garage, connected to the primary residence via a fully enclosed "breezeway". Breezeway connects basement of primary residence with 2 car garage, with inside stairs leading up to "cottage".

Front of cottage has a small deck, at upper grade level, and I understand need for external outlet there. Where is "rear" of cottage? Rear is garage level; grade is at front......

I read somewhere that outside outlets can no longer be connected to inside circuits, but can't seem to find a code reference. Anyone know where or if it is true? A dedicated circuit for one outlet on a deck?

Thanks for help!

Grov

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#190493 - 11/20/09 08:36 PM Re: Confused about outside outlet requirements [Re: Grover]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Grover:
I know of no requirement that an exterior receptacle cannot be on an 'inside' circuit, per NEC. There's a thread here that debates that subject, I don't remember if it was relocated into the "Non-US" forum or not.

IMHO, based on your description, there is no 'Rear'. However, you may decide to install a receptacle (GFI) on the rear garage wall to save any possible greif.

Is this structure still considered a single family dwelling, or is it considered a 'duplex', or two family? If it's a SFD, and a rear receptacle was required and installed when it was built, then that one (1) is all you need.
_________________________
John

Top
#190496 - 11/20/09 08:57 PM Re: Confused about outside outlet requirements [Re: HotLine1]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Grover,
Interesting point.
In my interpretation of "outside receptacle".
(Bear in mind I am from "out of town")

An outside receptacle would need it's own circuit (as in a home run) and be protected by a GFCI, no matter where it was on the outside of the building.

The receptacle will need weather-proofing.

That much might be true, but don't be too hard on me with the replies. grin
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#190499 - 11/20/09 09:48 PM Re: Confused about outside outlet requirements [Re: Trumpy]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
In the good old USA the outside receptacles can be on pretty much any circuit except the ones required to be dedicated (Kitchen, bathroom and laundry). You do need a GFCI.
Beyond that it is just a design decision
Commonly these come from basement or garage circuits since they will be GFCI.
I can make a case why dedicated circuits are good design tho
_________________________
Greg Fretwell

Top
#190500 - 11/20/09 11:15 PM Re: Confused about outside outlet requirements [Re: gfretwell]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Thanks for that Greg,
Am I assuming that "any" circuit could also encompass a lighting circuit as well?
Provided that the new connected load didn't over-load the existing circuit.

I'm here to learn things.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#190502 - 11/20/09 11:30 PM Re: Confused about outside outlet requirements [Re: Trumpy]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
Originally Posted By: Trumpy
Thanks for that Greg,
Am I assuming that "any" circuit could also encompass a lighting circuit as well?
Provided that the new connected load didn't over-load the existing circuit.

I'm here to learn things.


Mike the answer is Oui the outdoor recetpale can be on lighting circuit if not hevey loaded but normally it more common sense when upgrading the circuits in resdentail area the outdoor useally be on own circuits due some case I know some peoples go crazy with holidays luminaires or other pretty hevey stuff going on.

It simair to France but couple circuits that can not be used for outdoor recetpale Kitchen , Bathroom { this part is very strict }
and it mantory have RCD with weatherproof fitting on it.

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#190503 - 11/20/09 11:37 PM Re: Confused about outside outlet requirements [Re: frenchelectrican]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The strange thing about US residential circuit sizing is there are no rules. We are really only working with the 3va per square foot calculation and saying the load should be distributed across the general lighting circuits.
_________________________
Greg Fretwell

Top
#190505 - 11/20/09 11:43 PM Re: Confused about outside outlet requirements [Re: gfretwell]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
Gregg.,

The 3va per square foot that been written in NEC code cycle for super long time I don't really recall when the last time they change that and I have a funny feeling with engery pact they are tighen up the " noose " on genral lighting circuits.

I know in france it is 1.5 to 2 watts per sqfoot { I did converted from sqm to sqfoot } they change that requirement about 10 years ago

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#190509 - 11/21/09 07:49 AM Re: Confused about outside outlet requirements [Re: frenchelectrican]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Getting back to the OP, I believe that we're confusing two different code requirements.

The first would require a receptacle on the deca, if the deck is large enough.

The second - for outside receptacles to the building - applies only to 'grade level.' If one were to be requires on the door-ledd 'blind' side, it would be a requirement for the building in general, and not that particular unit.

IMO, there's no actual requirement that the required 'front' and 'rear' receptacles be on opposite sides of the building; I would allow them to be in the areas where they are likely to be usefull. (I admit that I'm very free in my interpretation here). I accept that it's possible for a particular site, by either design or geography, to make the 'opposite sides' idea absurd.

Nor does it help that -again - the illustration in the NEC handbook is in direct contradiction with its' caption.

Top
#190512 - 11/21/09 10:09 AM Re: Confused about outside outlet requirements [Re: frenchelectrican]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Marc, the thing that is inconsistent with a lot of other codes is, the NEC does not limit the number of outlets on a residential general lighting circuit. If the OP wants to tag the circuit on the other side of the wall for his outside receptacle there is really nothing stopping him.

Reno I agree sometimes trying to make a rigid "front and back" rule stick may be silly.
_________________________
Greg Fretwell

Top
Page 1 of 2 1 2 >



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals