#190353 - 11/12/09 01:16 PM 200amp disconect
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
I have a 400Amp service with 2 200Amp disconects. Can I put doouble barel lugs on 1 disconect to feed 1 200Amp panel and feed 100Amp back fed breaker.
Thanks H2O
Top
2017 / 2014 NEC & Related Books and Study Guides
#190354 - 11/12/09 01:47 PM Re: 200amp disconect [Re: watersparkfalls]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
My answer would be yes assuming your load is appropriate. Assuming also you are not overloading the 200a. overcurrent device and the 100a breaker is secured in the panel by a Listed clip.
_________________________
George Little
Top
#190355 - 11/12/09 03:12 PM Re: 200amp disconect [Re: George Little]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
The only joker in the deck is that the wire to the 100 amp panel should be sized for 200 amps, unless you can apply tap rules to your circumstance. Otherwise, there might be a problem fitting the wire into the breaker.
Top
#190357 - 11/12/09 04:16 PM Re: 200amp disconect [Re: renosteinke]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Reno- If I'm reading his post correctly, this would be a tap to a 200a Service switch. Since he is on the load side of fusing, we are talking feeder. In his case there are no actual feeder conductor, only double barrel lugs. This happens sometimes. Since he is terminating in a 100a overcurrent device he could use 100a. wire. The code reference could be 240.21(B)(1). There is no way he could overload the 100a. conductors since there protected due to the tap limitation mentioned above.


Edited by George Little (11/12/09 04:17 PM)
Edit Reason: Big fingers
_________________________
George Little
Top
#190367 - 11/12/09 11:12 PM Re: 200amp disconect [Re: George Little]
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
thanks guys.
H2o
Top
#190368 - 11/12/09 11:38 PM Re: 200amp disconect [Re: watersparkfalls]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I think Reno may be referring to the raceway requirements and 25' length restrictions for taps. The ampacity part is OK if this is a legal tap.
_________________________
Greg Fretwell
Top
#190369 - 11/13/09 08:14 AM Re: 200amp disconect [Re: gfretwell]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Thank you, Greg.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 89 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals