#190334 - 11/11/09 02:26 PM Exhaust fan in shower area??
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
Is an exhaust fan permitted in the shower? My customer has a shower that is totally separated by a wall and shower door from the bathroom area.
Also I assume I can put a recess light with a gasket in the shower. Does it have to be on GFI circuit. I'm only looking at the 99 code and do not have the newer ones available right now. Thanks..
Top
2017 / 2014 NEC & Related Books and Study Guides
#190335 - 11/11/09 02:41 PM Re: Exhaust fan in shower area?? [Re: sparkync]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Not a problem Sparky, But you need to look at the Listing. The fans that are suitable for use in a shower will be labeled "Suitable for use in a shower when installed on a GFCI protected circuit" or word to that effect. Beyond that you could be asking for trouble.
_________________________
George Little
Top
#190336 - 11/11/09 02:51 PM Re: Exhaust fan in shower area?? [Re: George Little]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Not only allowed, but required. You must have ventilation, unless there's a window you can open.

I say that, imagining a completely separate shower room. If you're simply describing a large glass shower door, then the existing bath fan might neet the HVAC code requirements.

Another possibility is a remote-operated fan. That is, a fan that is located somewhere the exhaust ducting, and not actually mounted on the ceiling of the shower.

If you do have a separate room, remember that the switches need to be outside the shower area itself - in the changing area, or even outside the room.
Top
#190339 - 11/11/09 05:41 PM Re: Exhaust fan in shower area?? [Re: renosteinke]
OreElect Offline
Member
Registered: 03/05/04
Posts: 98
Loc: Salem,Oregon.USA

On the fan subject.
We in oregon have had some changes.Bathrooms that have bathing facilities must have a min 80cfm max 3 sone controled by a timer,humidistat or auto control. Ducting to be smooth wall,no flex. This applies also for fan replacements.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals