The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 297 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#190334 - 11/11/09 02:26 PM Exhaust fan in shower area??
sparkync Offline

Registered: 10/17/02
Posts: 811
Loc: NC
Is an exhaust fan permitted in the shower? My customer has a shower that is totally separated by a wall and shower door from the bathroom area.
Also I assume I can put a recess light with a gasket in the shower. Does it have to be on GFI circuit. I'm only looking at the 99 code and do not have the newer ones available right now. Thanks..

2014 / 2011 NEC & Related Books and Study Guides
#190335 - 11/11/09 02:41 PM Re: Exhaust fan in shower area?? [Re: sparkync]
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Not a problem Sparky, But you need to look at the Listing. The fans that are suitable for use in a shower will be labeled "Suitable for use in a shower when installed on a GFCI protected circuit" or word to that effect. Beyond that you could be asking for trouble.
George Little

#190336 - 11/11/09 02:51 PM Re: Exhaust fan in shower area?? [Re: George Little]
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Not only allowed, but required. You must have ventilation, unless there's a window you can open.

I say that, imagining a completely separate shower room. If you're simply describing a large glass shower door, then the existing bath fan might neet the HVAC code requirements.

Another possibility is a remote-operated fan. That is, a fan that is located somewhere the exhaust ducting, and not actually mounted on the ceiling of the shower.

If you do have a separate room, remember that the switches need to be outside the shower area itself - in the changing area, or even outside the room.

#190339 - 11/11/09 05:41 PM Re: Exhaust fan in shower area?? [Re: renosteinke]
OreElect Offline

Registered: 03/05/04
Posts: 96
Loc: Salem,Oregon.USA

On the fan subject.
We in oregon have had some changes.Bathrooms that have bathing facilities must have a min 80cfm max 3 sone controled by a timer,humidistat or auto control. Ducting to be smooth wall,no flex. This applies also for fan replacements.