The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
01/18/17 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
ghost307 12
Trumpy 12
Who's Online
1 registered (Webmaster), 0 Guests and 73 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#190283 - 11/10/09 09:07 AM MC cable supported by ariel Cable . Amperage rate?
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
600 volt three conductor (310.20??), or 4160 three conductor(310.73??) either with messager.
Yoopersup

Top
2017 / 2014 NEC & Related Books and Study Guides
#190284 - 11/10/09 10:21 AM Re: MC cable supported by ariel Cable . Amperage rate? [Re: Yoopersup]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9062
Loc: Estero,Fl,usa
If the 3 conductors are in a metal jacket I don't think any "free air" table applies (one opinion).
_________________________
Greg Fretwell

Top
#190285 - 11/10/09 10:47 AM Re: MC cable supported by ariel Cable . Amperage rate? [Re: gfretwell]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
IMO: Not only do you use the 'standard' table (310.16), but you might even have to derate for heat (in the sun), as you wpould were they over a rooftop.

I believe the 2008 also would require this MC to be in a waterproof jacket as well.

Top
#190286 - 11/10/09 10:51 AM Re: MC cable supported by ariel Cable . Amperage rate? [Re: gfretwell]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
310.73 MV : In Isolated CONDUIT in air. So that one I;m pretty sure of.
310.18 LV : Not sure of?

Top
#190295 - 11/10/09 01:30 PM Re: MC cable supported by ariel Cable . Amperage rate? [Re: Yoopersup]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
For the 600V, I think you may need to use Table B.310.3 in Annex B, since it specifically mentions type MC cable in free air.
For over 2000V though, with three conductors, I believe you could use table 310.71, since IMO, the MC jacket is not actually a conduit or raceway as defined in Art.100.

Top
#190297 - 11/10/09 02:54 PM Re: MC cable supported by ariel Cable . Amperage rate? [Re: KJay]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
I probably should have said you may want to use Table B.310.3 in Annex B.

Top
#190314 - 11/10/09 08:40 PM Re: MC cable supported by ariel Cable . Amperage rate? [Re: KJay]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1308
Loc: Alaska
Just carious, why are you stringing MC on a messager? Or am just interpting something wrong here?
_________________________
"Live Awesome!" - Kevin Carosa

Top
#190324 - 11/11/09 10:17 AM Re: MC cable supported by ariel Cable . Amperage rate? [Re: sparkyinak]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
MC cable on Industrial sites is quite often put on poles to remote pumping stations ect. Both 600v & i;ve even see 15kv in MC on poles.
Yoopersup

Top
#190326 - 11/11/09 10:25 AM Re: MC cable supported by ariel Cable . Amperage rate? [Re: Yoopersup]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9062
Loc: Estero,Fl,usa
I have never seen it before either, which tends to explain my silly answer above, sorry for the confusion. wink
_________________________
Greg Fretwell

Top
#190330 - 11/11/09 12:58 PM Re: MC cable supported by ariel Cable . Amperage rate? [Re: gfretwell]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
mc cable 330.10 (B)4.

Installed outside of buildings or structures or as aerial cable.
type mc cable installed outside of buildings or structures or as aerial cable shall comply with 225.10,396.10,& 396.12.

Top