The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Yesterday at 04:48 AM
Temporarily feeding a panel...
by Potseal
09/29/16 11:05 PM
Massive power outage South Australia
by Meadow
09/29/16 06:46 AM
short circuit??
by Meadow
09/29/16 06:43 AM
Norwegian power?
by Meadow
09/29/16 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 12
sparky 10
gfretwell 8
Potseal 7
sparky66wv 6
Who's Online
0 registered (), 300 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#190138 - 11/07/09 10:14 AM Range cord vs circuit
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
I have an island(slab)with a range in it, I will need to pull thwn through my raceway to feed it, the manufactures specs say it has a maximum amperage of 27.6 amps and requires a 40 amp cord for connection. Can I feed a 40 amp plug with only 30 amps? Seems as an apprentice, my old company got gigged for this exact same thing. What say you?
Thanks,
H20

Top
2014 / 2011 NEC & Related Books and Study Guides
#190143 - 11/07/09 12:18 PM Re: Range cord vs circuit [Re: watersparkfalls]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
230.23

Quote:
(B) 30-Ampere Branch Circuits. A 30-ampere branch circuit shall be permitted to supply fixed lighting units with heavy-duty lampholders in other than a dwelling unit(s) or utilization equipment in any occupancy. A rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.
_________________________
Greg Fretwell

Top
#190147 - 11/07/09 01:56 PM Re: Range cord vs circuit [Re: gfretwell]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
What I have noticed, over the last several years anyway, is how difficult it is sometimes to decipher range manufactures listed installation instructions and electrical requirements.
Often they list a minimum circuit ampacity as well as a minimum conductor size that doesn’t seem to correspond directly to the nameplate rating of the appliance.

I can remember a couple of years ago with one dual-fuel range, the installation instructions said to install a 30A 4-wire receptacle in the location specified on the template, but when I read the actual electrical requirements in the instructions, they stated to use a #8 minimum conductor size for the branch circuit.

Because of this, I always try and get copies of the manufactures installation instructions whenever I get the appliance schedule for a job.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals