The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Webmaster > Admin
by Trumpy
01/20/17 08:29 PM
Live Chat Feature
by Admin
01/20/17 07:36 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 34
HotLine1 20
Ruben Rocha 17
Trumpy 16
gfretwell 15
Who's Online
5 registered (NORCAL, ComputerWizKid, Trumpy, Admin, tomn), 175 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#190025 - 11/03/09 01:05 PM Fire Pumps 695
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Em. Generator Breaker off that feeding service rated Firepump controller/Transfer Switch..
Service from Transformer feeding service rated fire pump controller/transfer switch (same).
From Generator Since breakers on Gen. Set its a Feeder.
From Transformer to to Service rated control/Transfer switch its Service conductors.
Generator side its 3 hots & Ground.
Transformer side its 3 hots & Neutal.(250.24C)
Neural & Ground terminate together at this point ????

Any one else run into this???
Yoopersup

Top
2017 / 2014 NEC & Related Books and Study Guides
#190054 - 11/04/09 11:04 AM Re: Fire Pumps 695 [Re: Yoopersup]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Originally Posted By Yoopersup
Em. Generator Breaker off that feeding service rated Firepump controller/Transfer Switch..
Service from Transformer feeding service rated fire pump controller/transfer switch (same).
From Generator Since breakers on Gen. Set its a Feeder.
From Transformer to to Service rated control/Transfer switch its Service conductors.
Generator side its 3 hots & Ground.
Transformer side its 3 hots & Neutal.(250.24C)
Neural & Ground terminate together at this point ????

Any one else run into this???
Yoopersup
If it's a delta generator, I hope it's a delta pump. If it's a delta pump, you don't need a neutral. 250.24(C) doesn't apply to delta panels, as the AC system is not grounded at any point.

Easy answer: don't run the neutral.

Top
#190058 - 11/04/09 12:39 PM Re: Fire Pumps 695 [Re: SteveFehr]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
480/277 Volt System at both Generator & Service Thus Neutral required per 250.24c to ist disconnect switch per code.Since Feeder Neutral is not required only equipment gr. But Service requires Neutral.
Yoopersup

Top