ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
fuse rejectors
by NORCAL. 03/29/17 01:44 AM
Old decora style outlets
by NORCAL. 03/29/17 01:41 AM
NFPA stuff
by gfretwell. 03/28/17 08:08 PM
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,847 Are you busy
166,733 Re: Forum
160,855 Need opinion
Who's Online Now
0 registered members (), 63 guests, and 12 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#190021 - 11/03/09 02:21 PM Mini Home Generator System Design  
wewire2  Offline
Member
Joined: Nov 2002
Posts: 244
California
A friend asked me to install a small 4 circuit transfer
switch little combo panel next to his sub-panel in his laundry room. The goal is to provide some lighting, a few outlets and keep the refrigerator going during a power outage. He has a typical 5000 watt portable generator with twist-lock and u-ground receptacles. How much circuit tracing and load calculating is typical in the planning of a small system like this. The homeowner knows he has limited power to only run the refer and a few lights.


Work Gear for Electricians and the Trades

#190022 - 11/03/09 02:38 PM Re: Mini Home Generator System Design [Re: wewire2]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,198
Chesapeake, VA
5000W will power everything in his house but the heat and hot water heater. I only have a 3500W, and I have to run around turning on lights to load mine down enough to drop it from 126 to 125V so my UPS stops beeping about the "high" line voltage. He could probably even run his stove or a modest (2-3 ton) heat pump on it, but not both at the same time.

If he's using an MTS, there are no load calculations required per NEC, he just has to be aware he has to open a few breakers on his panel before transferring to generator.

He may not even need a physical MTS; something as simple as shuffling breakers in his panel and installing a sliding piece of sheet metal that forces you to open the main breaker before closing the generator breaker is acceptable.


#190023 - 11/03/09 03:10 PM Re: Mini Home Generator System Design [Re: SteveFehr]  
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
WeWire2:

You can get a surprising amount of backup power from a typical 5KW generator. As always, you just have to be careful with load management. Mine covers my stove, water pump, ejector pump, sump pump, frezer, two refrigerators and just about all lighting/small appliance circuits. Granted, we can't fix Thanksgiving dinner and have all of the lights on at once, but it has never let me down. We also can't run the heat, water heater, washer/dryer or A/C at all, but beggars can't be choosers.

During one particularly long and frigid outage, we used a 1,500 watt portable heater in one room and spent most of our time in there. We did just fine.

I'm using a MTS on mine that is rated at 60 amps which feeds a 100 amp sub panel. If the load use gets carried away, I'll just turn off some of the branch breakers to prioritize the available power. In your situation with only four circuits, you should be just fine with even a 3.5KW generator. I'd be inclined to pick up a couple more circuits while I'm at it if I were you.

One thing that I've found to be valuable is to include the lighting circuit that serves the area of the panel(s) so that you can see what you are doing. I've also found that an emergency light set in this area helps to get things going without fumbling for flashlights.


---Ed---

"But the guy at Home Depot said it would work."

#190027 - 11/03/09 08:37 PM Re: Mini Home Generator System Design [Re: EV607797]  
wewire2  Offline
Member
Joined: Nov 2002
Posts: 244
California
If I'm getting this right, no load calculations are necessary for the feeder,xfer and mini-panel. Is this related to 702.5? system capacity and rating to supply all of the equipment "intended" to be operated at one time. The "intended" part gets you off the hook if the owner overloads the system? It just seems strange for the NEC to not require a formally designed system. This residential temp gen. stuff is a first for me and I'm trying to save a little digging time. Thanks for the input!


#190036 - 11/03/09 10:40 PM Re: Mini Home Generator System Design [Re: SteveFehr]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
something as simple as shuffling breakers in his panel and installing a sliding piece of sheet metal that forces you to open the main breaker before closing the generator breaker is acceptable.

I saw 1 for a square D, but can't find it again.

I suppose for a RESPONSIBLE electrician we could make one.

I'm using a 10 ckt gen tran right now. and 5500 honda-
I'm on a well and gas heat/HW and never had a problem (over a week some times)

This year I WILL have my CHRISTMAS lights on the generator.

Neighbors hate that. but warm up some nice rum spiced cider...... All is good again!!


#190037 - 11/03/09 11:26 PM Re: Mini Home Generator System Design [Re: leland]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Why do we make thinga harder than thay have to be? Has no one looked at a manual transfer switch?

I strongly reccomend the purchase of one ... there are enough little details to keep track of to make this a bit more involved than it seems, but here's the gist of it:

Imagine a SPDT switch, such as the 'hand-off-auto' switch on a control panel. This switch lets you choose between either 'in' to supply a single 'out'.

Our 'out' from the switch is the connection to the circuit were're feeding. The 'in' that is supplied by PoCo power comes from the usual breaker in the panel.

The other 'in' comes from a fuse or breaker mounted on out transfer switch, and is supplied by the generator.

Now, there is another complication, in that, IMO, you really want to switch the neutrals over at the same time. I like separately derived systems.

The grounds of both systems also need to be bonded together.


#190040 - 11/04/09 01:26 AM Re: Mini Home Generator System Design [Re: renosteinke]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,060
Estero,Fl,usa
I came up with an idea for my ex, who doesn't want any kind of "fancy" (read:expensive) transfer equipment. I told her to put a 3 way switch in place of the regular snap switch that functions as the disconnect for her furnace blower and flange mount plug out other side of the switch. Then in a power out situation she can just run an orange cord from the genny over to the furnace, flip the switch and she is good to go. A couple more cords for the fridge, the TV and a couple of lights gets her going.

Other than the 110.3(B) I am not sure where the problem is.


Greg Fretwell

#190043 - 11/04/09 02:13 AM Re: Mini Home Generator System Design [Re: gfretwell]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,313
Alaska
If the genset has an internal bond and the trailer is plugged into the main power source and running the genset can cause havoc with the power. A double bond can create CEMF in the wiring and have seen especially extension cords that were properly sized and used burn up without tripping the breaker. Odds are failure will not be that bad plus being you ex, then it is a sound way to go....JUST KIDDING! smile


"Live Awesome!" - Kevin Carosa

#190045 - 11/04/09 02:47 AM Re: Mini Home Generator System Design [Re: sparkyinak]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,060
Estero,Fl,usa
The generator is not bonded (Honda) but even if it was, the worst thing I can see is you would have some neutral current on the ground. Which wire would burn up?

I have seen plenty of improperly wired SDS transfer switches and no outward problems. As a practical thing it is the same as those 4 wire sub panels with a rebonded neutral.


Greg Fretwell

#190050 - 11/04/09 11:14 AM Re: Mini Home Generator System Design [Re: gfretwell]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
"No outward problem"

Yea, that's the kicker. I made a very easy-to-make mistake on a UPS system, and everything tested OK .... until there was an actual power failure, and some 120 circuits got 240 instead. There goes another tuition payment ....

Yet another reason to 'buy it' rather than 'build it.'


Page 1 of 2 1 2

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 16 (0.003s) Memory: 0.8204 MB (Peak: 1.0051 MB) Zlib enabled. Server Time: 2017-03-30 10:45:42 UTC