#189986 - 11/01/09 01:52 PM Blown Up Fuse
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
Quote:
I never heard what the actual cause was. So anyone's guess is as good as mine. It look's like an electrical arc might of melted the metal at the tops of the fuses a little bit.

Tristan S.



Top
Tools for Electricians:
#189987 - 11/01/09 04:09 PM Re: Blown Up Fuse [Re: Webmaster]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Damage appears to be on the line side of the fuse, possibly a line to ground fault. Or, severe overheating condition within the switching mechanism. Note there appears to be no damage on the load side terminations, or the load side of the fuse.
_________________________
John

Top
#189988 - 11/01/09 04:18 PM Re: Blown Up Fuse [Re: HotLine1]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Every fuse has a limit of how many amps it can safely interrupt. Exceed that, and this is what happens.

All it takes is a dead short - and more fault current available than the fuse is rated to interrupt. That's what all those 'fuse classes' are all about.

It's possible that the wrong type of fuse was used, but more likely that the fuseholder selection itself wasn't correct.

It's also possible that the PoCo made some changes - a new transformer, etc., that led to more current being available then there was before.

Top
#189995 - 11/01/09 09:39 PM Re: Blown Up Fuse [Re: renosteinke]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
The AIC rating will affect the safety blow thru the fuse so if the system was upgraded the AIC will go up and the fuse stay the same good chance it will really blow apart like you see at the photo ditto with breakers blink


I know Bussman fuse company did have a link or chart for AIC rating and it is good details in there.

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#190005 - 11/02/09 07:01 PM Re: Blown Up Fuse [Re: frenchelectrican]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Marc:

Bussmann Fuse has a wealth of info available...

www.bussmann.com

They have a few really good videos of fault current testing. Also, the 'Safety Basics' materials are informative and interesting.
_________________________
John

Top
#190356 - 11/12/09 04:07 PM Re: Blown Up Fuse [Re: HotLine1]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
I have seen heat related causes where a poor connection destroyed the fuse but never exceeded the ampere rating of the fuse. The tube is consumed over time from heating usually at the ferrule ends and eventually the guts get exposed. A fault cannot clear because all the arc quenching material has fallen out. The fact that the fuse tube is consumed on the top is part of my guess and i would look for silica sand in the bottom of the fuse holder to bolster or kill my theory. Also look for heat blued conductor or insulation damage like melting at the terminals. A Fault seldom causes slow failures and this looks like a heat failure with a fault at the end.