The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (ampherder), 184 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#189886 - 10/28/09 05:42 PM how to wire this?
adroga Offline
Member

Registered: 12/10/07
Posts: 35
Loc: canada
My friend has asked me to help him install a 5000 watt /240 V forced air heater in his new garage. I checked it out and it doesnt say if it comes wired internally with a Tstat, or if you need an external on.

Couldnt find if it had a relay inside to control the heat. So What kind of options do I have for an external Tstat? Do I absolutely need a relay wired up to the tstat ?

Are there any industrial tstats good for 5000W?

Thanks!

Top
2014 / 2011 NEC & Related Books and Study Guides
#189890 - 10/28/09 06:01 PM Re: how to wire this? [Re: adroga]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I'm sure there's a relay in there, but if it does, it won't look like a standard relay.

Baseboard heaters often have a resistor-typr relay in them. Let me explain how that works:

The thermostat is usually an 18vac circuit. When the t-stat closes, current flows through the resistor, making it hot. This heat causes the contacts to close, and the heater begins to make heat.

Because of this method of working, there is a significant delay between the t-stat closing, and the relay itself closing. You can usually hear a 'click' when it does.

I found it most helpful to place a thermocouple, or thermometer, in the heater fins, so I could readily tell if the fins were warming up or cooling down.

Another variation will have a t-stat mounted on the face of the neater, with a 2-pole switch right behind the faceplate. These switches are misleading, and very easy to mis-wire. I reccoment using your meter to ensure you understand which contacts belong to which wires.

Top
#189891 - 10/28/09 07:39 PM Re: how to wire this? [Re: renosteinke]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Adroga:
I believe that WW Grainger has a line voltage t'stat that is rated for 5KW at 240 volts.

I venture you are talking about a 5KW unit heater? Most mfg have a t'stat kit for their models, or a relay pkg to use a low volt t'stat

Or, if you have to be creative...a definite purpose 2 pole contactor/relay rated for 30 amp minimum, with a coil voltage of your choice, and a corresponding voltage rated t'stat should cover your needs.

Please check the Ca Electrical Code.
_________________________
John

Top
#189892 - 10/28/09 07:50 PM Re: how to wire this? [Re: HotLine1]
EV607797 Offline
Member

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
The only unit heaters of that size that I've ever wired called for a basic two-wire connection to the thermostat and like others have said, there is some form of contactor inside the unit. It is important that the feed not simply be controlled by a wall thermostat because the fan needs to be able to run after the heat is cut off. This allows it to cool down the element(s), just like with an electric furnace.
_________________________
---Ed---

"But the guy at Home Depot said it would work."

Top
#189894 - 10/28/09 09:33 PM Re: how to wire this? [Re: EV607797]
adroga Offline
Member

Registered: 12/10/07
Posts: 35
Loc: canada
Thanks for the replies. I didnt even consider that the fan needed to run after the heating element cuts off.

Its a ceiling garage heater on sale this week.. not sure if I can post the link..

http://tinyurl.com/yzug8j8

There is no brand of tStat for this heater..

I imagine there must me some sort of contactor inside. If the tStat is built in then can it just be wired straight to the panel or does it need a safety disconnect? The subpanel in the garage feeding the heater is only a few feet away.

Thanks for the great replies!

Top
#189905 - 10/29/09 06:22 AM Re: how to wire this? [Re: adroga]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Ed: (EV607797)

Good catch and important point re: fan run for cool down. I totally missed/forgot that
_________________________
John

Top
#189914 - 10/29/09 11:19 AM Re: how to wire this? [Re: HotLine1]
EV607797 Offline
Member

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
Originally Posted By: HotLine1
Ed: (EV607797)

Good catch and important point re: fan run for cool down. I totally missed/forgot that

No problem, John. That's what we are all here for.

Originally Posted By: adroga
If the tStat is built in then can it just be wired straight to the panel or does it need a safety disconnect?


My guess would be that as long as the disconnecting means is within sight, then no, a separate disconnect isn't needed. We'll need one of our Canadian friends to confirm that to be sure. Also, you'll need to check the name plate on the unit or the manufacturer's specifications to see what their requirements are. Some may even require fusing in the disconnect, though I seriously doubt it.
_________________________
---Ed---

"But the guy at Home Depot said it would work."

Top
#189925 - 10/29/09 04:47 PM Re: how to wire this? [Re: EV607797]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
If it plugs in or if the panel serving it is within 9 meters and in sight then it complies. Hard wired or out of sight requires a local disconnect simply because it has a motor in it.

Top
#189934 - 10/29/09 08:57 PM Re: how to wire this? [Re: mikesh]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
get the unit. then the specs.

Then worry about the 'what ifs'.

No 'what ifs' can be answered with out the 'this is what I have'.

Top
#190560 - 11/24/09 01:43 AM Re: how to wire this? [Re: leland]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Sorry to come in so late on this topic.

I used to install a lot of locally-made "Avon-Air" heaters, ranging from 2kW up to 45kW.

Yes you will need a contactor or two in there.

One thing that no-one else has mentioned is a control circuit to cut the power to the elements, if the fan motor fails.

Mind you, you'd think that would already be in the "box", I did get caught once with this.

That wasn't an Avon brand heater though, it was something the Boss bought cheap.

Food for thought though. bash