I've seen this happen over the years and have not really found a problem but maybe one time that I can think of. When an a/c comes on, the lights will dim momentarily
(just for a split second). Is this something that can be called normal or is there actually a problem hid in the circuit somewhere? I know if other appliances such as range, dryer etc... all are doing it, that there is a possibility of a loose neutral somewhere or even possibility of the power company loosing a phase or neutral somewhere, but I'm talking about just a momemtarily and slight dimming. The connections in the electrical panel have already been checked. Thanks for the input..
Top
Work Gear for Electricians and the Trades
#189846 - 10/27/09 02:22 PM Re: Lights dimming on a/c load?? [Re: sparkync]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
It is not unusual. There are a lot of things that can contribute to that. The size of the LRA on your compressor, the voltage drop in the service conductors and the transformer are a the main things. Those are really all out of your control. I don't really notice the lights dimming here except the ones on a dimmer but I do see the dip on the meter I have on the power.
_________________________
Greg Fretwell
Top
#189850 - 10/27/09 09:48 PM Re: Lights dimming on a/c load?? [Re: gfretwell]
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
My house was built in 2005, and my lights don't dim when the A/C kicks in. PG&E's transformer is very close though (on the other side of my neighbor's yard) and I believe it's a 25kva

I've performed service upgrades in older neighborhoods and had customers call saying their lights still dim, etc... and usually it's the poco trying to feed a whole block off of a 70 year old 15 kva transformer with 1/0 (or even #2) secondaries. (Anaheim and LADWP are notorious for this)

Only in SDG&E land did I ever see a poco upgrade their system after the city turned in final on the panel upsize.
Top
#189859 - 10/28/09 09:17 AM Re: Lights dimming on a/c load?? [Re: Lostazhell]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I have never seen a service drop larger than #2al for 200a or less.
_________________________
Greg Fretwell
Top
#189865 - 10/28/09 10:43 AM Re: Lights dimming on a/c load?? [Re: gfretwell]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
Dimming of incandescent bulbs goes by the square of the voltage, so even a small difference is voltage is amplified, and the human eye is very good at noticing even a tiny difference. It's normal and expected to have some voltage drop in the main feeders whenever a large motor load like a compressor starts up. The poco lines from the transformer to your house are the main culprit, I think. They're simply very small.
Top
#189939 - 10/29/09 11:41 PM Re: Lights dimming on a/c load?? [Re: SteveFehr]
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
Greg, I was referring to the "hardline" secondaries from the transformer feeding multiple drops going from pole to pole... a typical new construction 200A service here will get a 1/0 duplex and #4 or 6 for 100A here

San Diego actually upgrades the "pole to pole" duplex up to 4/0 from what I've seen
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals