#189199 - 09/23/09 01:49 PM 42-65 KAIC Rated Commercial Meter/Main Panels
wewire2 Offline
Member
Registered: 11/14/02
Posts: 244
Loc: California
My supplier cannot find a manufacturer that offers a 200A.
120/240V. meter/main commercial panel with test bypass that is rated over 22 KAIC. Anyone else run into this? Fused panels are available but the client wants breakers.
Top
Work Gear for Electricians and the Trades
#189200 - 09/23/09 02:39 PM Re: 42-65 KAIC Rated Commercial Meter/Main Panels [Re: wewire2]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Whats the impendence of the transformer???
22 k seems up there fer 120/240 volt single phase>??
What K is readly available??
Top
#189201 - 09/23/09 02:59 PM Re: 42-65 KAIC Rated Commercial Meter/Main Panels [Re: Yoopersup]
wewire2 Offline
Member
Registered: 11/14/02
Posts: 244
Loc: California
22K panels are usually in stock. I am getting the specified AIC ratings off of the engineered drawings or utility reports. Seems like most of the jobs we do are 42-65 K rated.
Top
#189205 - 09/23/09 04:05 PM Re: 42-65 KAIC Rated Commercial Meter/Main Panels [Re: wewire2]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
If impendence is less then Aprox. 2.2 then you gotta jump up to 22000 .
50 kva secondary 208amps.
2.2 at 208 volts single phase. APROX.
I get APROX. 9454 , Its less if a distance away.
Check with Eng. But power companys always go high so do designers. You never wanna be lower then whats really required!!!!
Top
#189206 - 09/23/09 04:55 PM Re: 42-65 KAIC Rated Commercial Meter/Main Panels [Re: Yoopersup]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
Did you check with Sq.D ?

_________________________
John
Top
#189207 - 09/23/09 05:24 PM Re: 42-65 KAIC Rated Commercial Meter/Main Panels [Re: HotLine1]
wewire2 Offline
Member
Registered: 11/14/02
Posts: 244
Loc: California
Tried Square D. B-line, Cutler Hammer, Milbank.
Top
#189216 - 09/23/09 11:21 PM Re: 42-65 KAIC Rated Commercial Meter/Main Panels [Re: wewire2]
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
RSE Sierra

If they don't have it, they'll manufacture what you need for your specs.... I believe they use Siemens gear
Top
#189217 - 09/23/09 11:43 PM Re: 42-65 KAIC Rated Commercial Meter/Main Panels [Re: Lostazhell]
wewire2 Offline
Member
Registered: 11/14/02
Posts: 244
Loc: California
I wonder why special order was not offered as an option. I'll have to check that one out. Thanks!
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 85 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals