#189034 - 09/16/09 01:35 PM A GOOD Working Space Violation?
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
Here is a pic of a panel I recently saw. The sump pit is more than 36" from the wall, but that discharge pipe does cross the required 'working space:'



Some might argue that having the pipe there is a good thing, as it will discourage folks from stacking stuff in front of the panel. Others might see the pit as blocking access to the panel. (FWIW, you can NOT stand on that pit cover). What say you?

Top
Tools for Electricians:
#189040 - 09/16/09 03:56 PM Re: A GOOD Working Space Violation? [Re: renosteinke]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I would like to see a cover you could stand on but I would have a hard time citing it.
The pipe is a trip hazard tho and you do not have "clear space". That would need to be fixed
_________________________
Greg Fretwell

Top
#189046 - 09/17/09 07:26 AM Re: A GOOD Working Space Violation? [Re: gfretwell]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 876
Loc: Chicago Illinois USA
I think that adding an elbow to the discharge pipe to kick it to the left would get it out of the way and get the trip-free workspace that we would all prefer.
The only tripping hazard then would be the cords to the sump pump, but I should think we be able to work around that easily enough.
BTW, in my stepfather's house we put the sump pit (with a sturdy cover) right in front of the panel...nothing ever got stored there.
_________________________
Ghost307

Top
#189049 - 09/17/09 11:41 AM Re: A GOOD Working Space Violation? [Re: ghost307]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
A more elegant solution would be a wooden platform (a pallet?) over the whole mess that would be removable to service the sump and give a good non-conductive work surface but that is far beyond what an inspector could request.
_________________________
Greg Fretwell

Top
#189050 - 09/17/09 12:39 PM Re: A GOOD Working Space Violation? [Re: gfretwell]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
The irony is that - whether you move the pipe orbuild a platform - you'll also make the place 'just rigt' for storing the Christmas decorations.

Top
#189051 - 09/17/09 01:08 PM Re: A GOOD Working Space Violation? [Re: renosteinke]
electure Offline

Member

Registered: 12/24/00
Posts: 4225
Loc: Fullerton, CA USA
The Christmas decorations can be moved. The pipe is a permanent obstruction.

If there's going to be a workspace violation anyway, I'd rather move the Christmas decorations.

Either way this is not a "good" thing.

Top
#189062 - 09/17/09 07:02 PM Re: A GOOD Working Space Violation? [Re: electure]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
An 'existing' condition in a large townhouse complex (+/- 350 units). The pit is there, the discharge is off to the right, so no trip. Some have Greg's idea of a 'platform', some have fitted covers that are part of the radon remediation, some have...nothing!

As Electure said...stored items can be moved, although it a pain in the butt; and two existing 'wrongs' can be corrected.
_________________________
John

Top