The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 254 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#189016 - 09/15/09 02:06 PM SER Cable
jem Offline
New Member

Registered: 04/30/07
Posts: 8
Loc: nc
Old method for 200 amp residemtial service. 200 amp Main lug Meter combo. Pull larger 240 Volt loads outside to meter combo and run 100 amp feeder (#1 aluminum SER cable) to subpanel in the intereior of the house. The changes to Article 338 seem to say that this #1 SER cable will be now be limited to 85 amps because it is being used as an interior wiring method(from the disconnect on the outside of the house through the crawlspace to an interior panel). Am I reading this correctly.

Top
2014 / 2011 NEC & Related Books and Study Guides
#189018 - 09/15/09 07:04 PM Re: SER Cable [Re: jem]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
That's the way I see it also. If you follow the reference to part II of Article 334, then you're limited to the ampacity in the 60 degree column & that is 85 amps.

I looked up the ROP from the 2008 code cycle & it appears that this was the intent. If you think about it, both cables are very similar with the SER having an outer jacket that is a little tougher than NM.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#189019 - 09/15/09 09:57 PM Re: SER Cable [Re: Tom]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I read the recap of the 2011 changes in the IAEI magazine and they are doing away with the whole "feeder" language in 310.15(B)(6) so you are going to have more surprises when it comes to feeders, even if they do carry the whole house load. Basically that table will only apply to service conductors if I read the change right.
Couple this with the 338 change and you are running 4/0 Al SER for a 150a disco outside to a 150A L&A panel inside.
If you have a 200a you won't be able to use SER at all
_________________________
Greg Fretwell