#188879 - 09/08/09 08:24 AM 480V on push button controls.
gscott Offline
New Member
Registered: 09/04/09
Posts: 3
Loc: Chicago
Years ago I had to remove all 480V controls from out motor control centers and push button locations. The subject has come up again and I can't find anything that showes this being against code. I have not found anything NEC, NESC or OSHA. Can someone en lighten me on the subject.

Top
2017 / 2014 NEC & Related Books and Study Guides
#188880 - 09/08/09 11:10 AM Re: 480V on push button controls. [Re: gscott]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I can't think of any reason why it would not be code conforming if they followed the rules. Bear in mind, this is the same voltage to ground as your 277 lighting and that is just a snap switch in a box.
_________________________
Greg Fretwell
Top
#188881 - 09/08/09 02:28 PM Re: 480V on push button controls. [Re: gfretwell]
gscott Offline
New Member
Registered: 09/04/09
Posts: 3
Loc: Chicago
For the most part these circuits are not fused, they come directly off the equipment fuse and can have fuses up to your larges horsepower. Ther has to be an arc flash issue.
I found this on www.msha.gov

30 CFR 18.47
Voltage limitation.

(a) A tool or switch held in the operator's hand or supported against his body will not be approved with a nameplate rating exceeding 300 volts direct current or alternating current.

Top
#188882 - 09/08/09 02:59 PM Re: 480V on push button controls. [Re: gscott]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Is that 300v phase to phase or to ground?
480 wye is 277 to ground and I suspect that is where the 300v limit comes from.
I had the impression we were talking about panel mounted switches, not hand held. If this is a hand held dongle I can see your concern.
If people are not working on this equipment with the covers off, I don't think arc flash is that big an issue. I am assuming you are talking about the operator, not the maintenance staff.
The enclosure around equipment should contain the flash/fire. Isn't that part of the listing? The switch itself is not the motor starter is it? I do see that fusing the coil lead would be useful. If you don't you are bumping up against the fixture wire sizing rules.
_________________________
Greg Fretwell
Top
#188883 - 09/08/09 05:16 PM Re: 480V on push button controls. [Re: gfretwell]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
If its a 480 volt 3 phase motor odds are theres no 277 volt to ground (to switch) & even if there was you can't switch the grounded conductor.
Part VI in 2005 is area that deals with this as far as what I've found.
Yoopersup
intersting question I always took it for granted that 480volt CAN NOT be field switched, if so then limit switchs , ect????
Top
#188897 - 09/09/09 07:02 AM Re: 480V on push button controls. [Re: gscott]
gscott Offline
New Member
Registered: 09/04/09
Posts: 3
Loc: Chicago
I was talking about push buttons, The operator is the one to protect. Limit switches and other devices I am not so concerned with. A 480v wye will be 277v to ground but a open delta will very and could be over 300 volts. sounds like it is ok to use 480v control on push buttons, but a control transformer to 120v just seams alot safer.

Gary
Top
#188903 - 09/09/09 10:48 AM Re: 480V on push button controls. [Re: gscott]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
If you are changing out the motor controller contactors, why not just go to a 24v system? 120v is only marginally safer than 277.
_________________________
Greg Fretwell
Top
#188904 - 09/09/09 11:19 AM Re: 480V on push button controls. [Re: gfretwell]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA

The problem lies with the contact blocks behind the pushbuttons.
Most (not all mind you) are rated for 300 Volts.

It will probably pay to check
Top
#189296 - 09/30/09 02:22 AM Re: 480V on push button controls. [Re: electure]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
208V / 480 V systems stink...

Too many problems with back-EMF in motor controls.

Give me 120V, 24V, 277V any day.

Back-EMF results in contactor chatter and other problems.

Ungrounded control circuits are a HEADACHE.
_________________________
Tesla
Top
#189299 - 09/30/09 03:18 PM Re: 480V on push button controls. [Re: Tesla]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
I wouldn't personally use "Mains voltage" for a control circuit, although in some cases you don't really have a choice.

I prefer something like 24V, fed from the secondary side of a double-wound transformer, as long as there are fuses in both sides of the winding, I don't see an issue.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals