#188851 - 09/07/09 12:51 AM Panel disconnect required in single tenancy
bigpapa Offline
Member
Registered: 03/18/06
Posts: 77
Loc: canada

This might be just in BC but BCSA directive D-E3 070302 6 states
that a single commercial or residential tenancy would have to have its own main disconnect. I was once told to upgrade an existing load center to a main breaker panel in a renovation that was quite substantial but since then I have never been asked.
My question is where do they draw the line? Which renovations should include a panel upgrade and which ones will be grandfathered. My opinion is that if the panel is existing then it stays as is.

What are your experiences with this?

Here is the text from the directive:

1. In multi-unit buildings where the feeders are supplied from an electrical distribution that is
in a separate building, room or enclosure the requirement for over-current devices and
control devices to be “readily accessible” is not being met. Interpretation of Rule 14-406 is
to require installation of a single main disconnecting means for the loads within the area of a
single tenancy, ownership, etc. (occupancy). In multi-unit buildings where the feeders are
supplied from an electrical distribution that is in a separate building, room or enclosure,
each occupancy is to be provided with a main disconnecting means that is within the
occupancy. This requirement is intended to improve safety by providing ready access by a
qualified person to the single disconnecting means controlling all electrical equipment inside
the occupancy.
Top
Tools for Electricians:
#188855 - 09/07/09 09:59 AM Re: Panel disconnect required in single tenancy [Re: bigpapa]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
Not required in Saskatchewan. That "interpretation" is a pretty big saddle to put on this little horse:

14-406 Location of control devices
(1) Control devices, with the exception of isolating switches, shall be readily accessible.
(2) Remotely controlled devices shall be considered to be readily accessible if the means of controlling them are readily accessible.

Isn't the main an isolating switch?
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 65 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals