The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 18
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 245 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#188726 - 08/29/09 09:57 AM Main service circuit breaker or 6 feeder circuits?
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
A service with a main distribution panelboard with a main circuit breaker and 6 or less feeder circuit breakers. Is the main circuit breaker redundant, a potential weak point, or a good idea?
(assume no need for future expantion)

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#188728 - 08/29/09 12:22 PM Re: Main service circuit breaker or 6 feeder circuits? [Re: cgw]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
I have encountered this situation twice recently.

One was a strip mall where the owner wanted to divid his largest space. This project became untenable, simply because of the work that would be required to separate / upgrade the electric for the new spaces. In building the strip mall, every trick had been used to keep the required meters / disconnects to a maximum of six - and adding the main disconnect that additional meters would have required in turn meant the wholesale replacement of the entire switchgear.

In hindsight, it would have been far better had the main disconnect been included at the start. That's what happens when you use the NEC as a design manual!

The other job was the opposite situation; I added a 'main' before just one service. Why? Because there are plans to add two more, and having the disconnectwill make the future work much easier to do.

IMO, a good design allows for future uses, and makes provisions for future maintenance work. While a good design is almost certain to meet code, a 'code minimum' design may be poor design.

Top
#188744 - 08/30/09 10:24 AM Re: Main service circuit breaker or 6 feeder circuits? [Re: renosteinke]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
I will echo what reno said, do a good design that is practical for now and plan for future.
_________________________
Be kind to your neighbor, he knows where you live


Top
#188745 - 08/30/09 10:28 AM Re: Main service circuit breaker or 6 feeder circuits? [Re: cgw]
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
In my case it is a single owner building with the meter before the MDP. Right now 5 feeders out of the MDP. There is space for for a feeder circuit breaker large enough for any conceivable addtion. (that would bring it up to 6 if it ever happened). Is there any good reason to have a main circuit breaker in the MDP.

Top
#188747 - 08/30/09 11:17 AM Re: Main service circuit breaker or 6 feeder circuits? [Re: cgw]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
Heck yes.

First of all, that main disconnect is another place you can add a fuse - one way to keep track of problems. There's no way that feeder can supply everything to maximum load.

Secondly, the main disco gives you a way to work on the system without having to cut the PoCo wires at the weatherhead.


Here's a pic of a place that just kept growing:




Edited by renosteinke (08/30/09 11:21 AM)

Top
#188752 - 08/30/09 07:07 PM Re: Main service circuit breaker or 6 feeder circuits? [Re: renosteinke]
WireNuts29 Offline
Member

Registered: 07/24/07
Posts: 85
Loc: Mass, U.S.A.
aghhh!!

Top
#188774 - 08/31/09 10:10 PM Re: Main service circuit breaker or 6 feeder circuits? [Re: WireNuts29]
JoeTestingEngr Offline
Member

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
What about the advantage of knowing what your overcurrent protection is by the size of your main breaker or fusing?
Joe

Top
#188776 - 09/01/09 08:09 AM Re: Main service circuit breaker or 6 feeder circuits? [Re: JoeTestingEngr]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
Depends upon WHERE the main disco is located. If it's on the PoCo side of the meters, you won't have access to the fuses.

Top
#188778 - 09/01/09 01:47 PM Re: Main service circuit breaker or 6 feeder circuits? [Re: cgw]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Point of Info.
230.90 (A) Exception # 3.
Allows the six disconnects to total more then the service conductors ampacity.(see calculated load requirements).
Example service conductors good for 3200 amps with six
600 amp breakers . This is done quite often so the GFI rule does not come into effect.(230.95)
Yoopersup