#188705 - 08/27/09 08:35 AM Fire Caused By Meter Arc?
Zapped Offline
Member
Registered: 10/01/02
Posts: 482
Loc: Huntington Beach, CA, USA
Top
Work Gear for Electricians and the Trades
#188708 - 08/27/09 09:49 AM Re: Fire Caused By Meter Arc? [Re: Zapped]
sabrown Offline
Member
Registered: 12/12/02
Posts: 302
Loc: Ogden, Utah, USA
As I have learned many times, newspapers seldom (if ever) report official versions of anything. This can easily be viewed as a dumbed down report of what was possible actually related to the reporter.
Top
#188710 - 08/27/09 11:11 AM Re: Fire Caused By Meter Arc? [Re: sabrown]
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
That is exactly what I'm thinking. Just like when the press reports the cause of a fire to be "electrical" when in fact it was due to an overloaded 18/2 extension cord. That's not an electrical fire. It is a fire caused by carelessness.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#188711 - 08/27/09 04:59 PM Re: Fire Caused By Meter Arc? [Re: EV607797]
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Well, actually, that 18/2 extension cord is an electrical fire. That is the way that the statistics are gathered. An electrical appliance that starts a fire is also an electrical fire.

A long time ago, EC&M, I think, ran an article that was titled" All Those Electrical Fires, Hogwash." In the article, the author referred to a fire report that stated the cause of the fire could not be determined because the building wasn't wired.
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#188712 - 08/27/09 05:05 PM Re: Fire Caused By Meter Arc? [Re: EV607797]
Alan Belson Offline
Member
Registered: 03/23/05
Posts: 1803
Loc: Mayenne N. France
I'm not familiar with American 'aluminum siding', but would it not need to be grounded in some way for safety?
_________________________
Wood work but can't!
Top
#188714 - 08/27/09 05:55 PM Re: Fire Caused By Meter Arc? [Re: Alan Belson]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Alan, there is absolutely no requirement to make any manner of ground or bond between the electrical system and the metal siding.

As our code reads, only metal 'likely to become energized' must be bonded, and most often this is done within an appliance.

Now, our meter cans are metal, and household siding, metal roofs, and all manner of things are nearly impossible to instal without there being some manner of path to ground.

I've seen some pretty impressive scorch marks result when a service mast breaks, and the results of some pretty severe arcing when a meter base fails. I don't doubt that a fire COULD be caused this way.

Yet, I suspect that the news story has left out some information, and we're not getting the full story.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 59 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals