#18856 - 12/15/02 05:59 PM bonding gas line
ga.sparky56 Offline
Member
Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
In my area, all gas piping is done by the propane company. They are using "trac-pipe" which looks like metallic liquidtite only with a yellow coating. Runs all the way to furnace or WH. Except for avery short pipe nipple in some cases there is noplace to put a clamp. any suggestions? No AHj or inspections here. Thanks in advance.
Top
Work Gear for Electricians and the Trades
#18857 - 12/15/02 07:08 PM Re: bonding gas line
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Bonding gas lines is accomplished through the equipment that is likely to energize the line. Example: the furnace that this line goes to has an equipment ground that serves the furnace. This also bonds the piping because it is connected to the furnace as well.
Top
#18858 - 12/15/02 09:02 PM Re: bonding gas line
ga.sparky56 Offline
Member
Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
Thanks Scott, what we usually run into here is the heating/ac guys will put acord and plug on the furnace, and we are expected to put a recep next to the furnace,unplug cord no more bond. Iguess we should insist on a disconnect/hardwire setup. This area is very similar to what sparky66wv deals with. We get alot of heat for trying to comply with nec.
Top
#18859 - 12/16/02 03:44 AM Re: bonding gas line
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
If you unplug the equipment that is likely to energize the piping you lose your bond. You also don't have equipment likely to energize the piping. So is there a seperate bond required in this case? I am not sure.
Top
#18860 - 12/16/02 04:22 AM Re: bonding gas line
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
ga.spark,

A cord & plug for a furnace would appear to violate 400.7 (8).
Is this practice common with anyone else?
Top
#18861 - 12/16/02 05:39 PM Re: bonding gas line
ga.sparky56 Offline
Member
Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
Redsy Ithink you are right,afurnace is probably not listed for use with acord and plug.I will not be guilty of this again. But what if I have say one or two fireplaces with gas logs with no electrical hookup? Do I need to find amethod to bond this?
Top
#18862 - 12/17/02 07:16 AM Re: bonding gas line
classicsat Offline
Member
Registered: 11/23/02
Posts: 449
My brother's gas water heater has a factory
cord/plug. In fact, all the assisted vent gas WHs I've seen has factory cord/plugs on them.
Top
#18863 - 12/17/02 07:26 AM Re: bonding gas line
ayrton Offline
Member
Registered: 12/21/01
Posts: 205
Loc: Pa
Why would you "bond" gas pipe? In Art 250-52B (1) Metal undrgrnd gas pipe as no no.
Understand you are not talking about underground, but don't you think making gas line a ground could be a hazard?
As a rule I never use a gas line of any kind to bond!
Top
#18864 - 12/17/02 08:31 AM Re: bonding gas line
caselec Offline
Member
Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
ayrton - Read 250.104(B) for your answer.
_________________________
Curt Swartz
Top
#18865 - 12/17/02 11:37 AM Re: bonding gas line
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
ayrton,
You appear to be confusing the bonding (250-104) of the gas pipe with using it as a grounding electrode (250.52(B)(1). You can't use the undergroud gas piping as a grounding electrode because that could create a hazard for the gas company if there was a current flow and they took the pipe apart. It would also interfer with their cathodic protection of the underground metal gas piping. The gas companies install dielectric fittings between the undeground and interior piping systems. The interior gas piping must be bonded to prevent a shock hazard. If a gas appliance with an electrical connection would have a ground fault, or if an improperly installed cable would fault to the gas pipe, the bonding would prevent a shock hazard. Note that this bonding is also required by the Fuel Gas Code, not just the electrcial code.
Don
_________________________
Don(resqcapt19)
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
2 registered (dougwells, Admin), 190 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals