The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 17
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
1 registered (geoff in UK), 231 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#188537 - 08/16/09 11:45 AM Single 120V ckt, GFCI, underground to tool shed ?
glene77is Offline
New Member

Registered: 11/17/07
Posts: 4
Loc: Memphis, TN
(1) Does NEC allow a single 120V ckt to be run to an exterior tool/storage shed via GFCI control, having only a Simple Disconnect in the tool/storage shed? NEC cites?
(2) Using UF cable, What is the depth requirement?

I have answers, but want to check myself.

glene77is
_________________________
Glene77is @ Memphis, TN
Electrical Science & Engineering.

Top
2014 / 2011 NEC & Related Books and Study Guides
#188538 - 08/16/09 12:11 PM Re: Single 120V ckt, GFCI, underground to tool shed ? [Re: glene77is]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
If the GFCI protection is on the line side of the excavation at a 1&2 family dwelling the answer is 12" depth 300.5.
The exception to 250.32(A) allows you to skip the ground electrode system for a single circuit but 225.31 does not give you relief on the disconnect.
_________________________
Greg Fretwell

Top
#188539 - 08/16/09 04:46 PM Re: Single 120V ckt, GFCI, underground to tool shed ? [Re: gfretwell]
luckyshadow Offline
Member

Registered: 01/04/05
Posts: 305
Loc: Maryland USA
a basic single pole snap switch will work as a disconnect

Top
#188541 - 08/16/09 05:32 PM Re: Single 120V ckt, GFCI, underground to tool shed ? [Re: luckyshadow]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
I hate to say this, but you were in violation of the NEC the moment you asked the question.

Why? Because the NEC, as detailed in Article, is NOT a design manual. The moment you try to 'design to code,' you're off to a bad start.

Apart from that, there are other considerations.

For example, the depth you bury the cable is influenced by what use the ground over the cable gets, and what else is there to protect the cable. You're not doing yourself any favors if the cable is damaged every time the gardener works on the lawn sprinkler system. In a nutshell, "Deeper is better."

Likewise, good practice might suggest a 'handhole' or junction box at either end of the run. This will help you avoid having tom open walls later if you need to replace the cable. (Maybe I should make that "WHEN" you need to replace the cable). The junction boxes also make it easier to identify exactly where the cable lies. There's no 'law' that says you must do this, but it might be a smart thing to do.

Then there's the matter of Murphy's law. One light becomes a light and a receptacle, then a workbench full of power tools, then you want heat ... before you know it, you're out there digging again. I don't know about you, but I hate digging - and customers don't like the scar left over the trench. So, I really like to run wires in pipe, rather than UF cable. Bury the pipe deep, so the roto-tiller doesn't hit it. Since PVC pipe is cheap, there's no reason to run anything smaller than 1". There's then plenty of room for future additions.

Trench depth is something frequently modified by local ordinance. For example, in my very, very rocky area the city still wants everything buried 24".

Finally, even though listed means of splicing direct-buried cable exist, my experience suggests that you really, really want a handhole for your splices. If nothing else, this gives you an access point for future troubleshooting.