I couldn't find in section 408 that talkes about breakers on the left are odd numbered and the breakers on the right are even numbered. Is this a code requirement?
I installed a subpanel from SQUARE-D that had the option of being installed with the Main lugs down or up. So I installed it the way that was convenient for the existing wiring and the existing feeder. Then when i installed the cover the upper left breaker was #12, upper right breaker was #11.
408.3(E) is phase arrangement only, i didn't see anything in 240 or 404. the only issue i find is with 110.3(B) which i should be O.K.
Is this a violation of NEC?
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
Not a violation. There isn't even anything that says you have to number the circuits, you could use letters or make up a bunch of symbols. I've even seen the left side numbered 1 - 22 and the right side 23 - 42.
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
Most resi panels have 'numbers' stamped into the deadfront (cover), and a factory directory on the door, or on the cover. The directory should 'match' the factory numbers, or the directory should match the breaker ID that you install.
The only NEC Article is 110.3 (b).
John
|
|
|
|
Joined: Jul 2001
Posts: 599
Member
|
No.
As you said, the panel is designed that way.
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
I think it comes from English being read left to right and top to bottom. I would think that panels in Japan and Israel would be numbered differently since they read somewhat differently than most of us on this forum are used to.
Ghost307
|
|
|
|
Joined: Aug 2006
Posts: 356
OP
Member
|
Ghost307, That is a good point. i never thought about it that way.
Thank you all for your comments.
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Jul 2007
Posts: 1,335
Member
|
Most, but not all panels are listed for mounting in either direction. Check before you do. As for the numbering method, that is a industry standard, not a code requirement. I can not quote you the origin though. Panels use to be numbered starting on the left going down then continued on the right. If there was two or three pole breaker in the mix, that counted only as one circuit.
"Live Awesome!" - Kevin Carosa
|
|
|
|
Joined: Jul 2001
Posts: 599
Member
|
Square D' I-Line panel has no numbering on the trim/dead front at all.
|
|
|