The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (aussie240), 158 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#188216 - 07/25/09 11:00 AM Romex outside
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
I've got a picnic shelter I'm giving a price on that will include lighting and a few receptacles. The wiring will not be exposed to the direct weather but will be exposed to humidity. Can regular romex be used or do I need to use UF cable ?? thanks..

Top
2014 / 2011 NEC & Related Books and Study Guides
#188217 - 07/25/09 11:43 AM Re: Romex outside [Re: sparkync]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Judgment call for sure. The '08 NEC has some new wording in 334.14(B)(4) that might apply since the code prohibits installation in damp locations. More than likely most most inspectors would buy it.

As a side note can anyone show me where the conductors in NM cable are identified as THHN?

334.14(B)(4)

_________________________
George Little

Top
#188220 - 07/25/09 01:48 PM Re: Romex outside [Re: George Little]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I don't think NM-B has ever been allowed in damp locations.

I always believed it was because of the kraft paper packing that will wick up water.
The only question for the AHJ is how damp is that location?

Quote:
Location, Damp. Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations...
_________________________
Greg Fretwell

Top
#188221 - 07/25/09 01:51 PM Re: Romex outside [Re: sparkync]
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Also since the outlets will be under the shelter on the inside of the post, will I need to use in use covers or just regular weatherproof outlet covers? Thanks.

Top
#188222 - 07/25/09 01:55 PM Re: Romex outside [Re: gfretwell]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
They are not "THHN" they are just a 90c rated conductor of some kind, since that is all the listing commits to.

As a practical thing we might assume they are THHN, just because of manufacturing expediency but we can't prove it.
For that matter you might even assume they are THHN/THWN but you know what assume means.

Who would have thought the covers on NM conduit bodies and the straps for RNC were not made out of the same plastic as the raceway but I had a Carlon rep tell me they don't have to be (in the listing) and in fact, at the time they were not UV protected. I don't know if they ever fixed that.
_________________________
Greg Fretwell

Top
#188223 - 07/25/09 01:58 PM Re: Romex outside [Re: gfretwell]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I think snap covers would be appropriate.
_________________________
Greg Fretwell

Top
#188231 - 07/26/09 11:50 AM Re: Romex outside [Re: sparkync]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
from the southwire PDF for the romex product.

APPLICATIONS
Southwire's Romex SIMpull Type NM-B (nonmetallic-sheathed cable) may be used for both exposed and concealed work in normally dry locations at temperatures not to exceed 90C (with ampacity limited to that for 60C conductors) as specified in the National Electrical Code 1 . NM-B cable is primarily used in residential wiring as branch circuits for outlets, switches, andvother loads. NM-B cable may be run in air voids of masonry block or tile walls where such walls are not wet or damp locations. Voltage rating for NM-B cable is 600 volts.
_________________________
Be kind to your neighbor, he knows where you live


Top
#188242 - 07/26/09 09:16 PM Re: Romex outside [Re: Niko]
jdot77 Offline
Member

Registered: 03/06/07
Posts: 16
Loc: Riverview, Fl
I would say no to romex in that location because it would be considered damp. Also your are in a damp location for the cover as well not a wet location subject to pounding rain so a flip up wheater proof cover should be fine.
_________________________
jason

Top
#188257 - 07/27/09 03:38 PM Re: Romex outside [Re: jdot77]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
If it were me, I would spec Type UF, but with work being as tight as it is these days, maybe check with the local inspector so you don't price yourself out of the job if somebody else is bidding it in NM and knows for sure the inspector will allow it.
As they say... when in Rome...

Top
#188262 - 07/27/09 06:33 PM Re: Romex outside [Re: KJay]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Quote:
As they say... when in Rome...


... use Romex?
_________________________
Greg Fretwell

Top