#188087 - 07/21/09 08:38 AM gas pipe used as grounding electrode
Chris Rudolph Offline
Member
Registered: 05/01/01
Posts: 160
Loc: Winter Park,Fl USA
I have updated the service,150 amps,breaker panel,and installed a new grounding system in a single family house with basement in Upstate New York.The inspector said all was done well except that I had to clamp the grounding electrode conductor to the gas pipe in the basement.
Is this a violation of NEC 2002 250.52 B 1?
Chris
Top
2017 / 2014 NEC & Related Books and Study Guides
#188089 - 07/21/09 09:28 AM Re: gas pipe used as grounding electrode [Re: Chris Rudolph]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
That is not the ground electrode, it is bonding the gas pipe (250.104(B))
He also could have said you bond to the circuit EGC "likely to energize" the pipe. That will usually be the largest piece of electrical equipment connected to the gas pipe. (range electric igniter, furnace blower etc)
He might even say that was the A/C compressor via the freon line set to the A coil in the furnace. The safest alternative is the GEC, then all bases are covered.
_________________________
Greg Fretwell
Top
#188103 - 07/21/09 01:14 PM Re: gas pipe used as grounding electrode [Re: gfretwell]
Chris Rudolph Offline
Member
Registered: 05/01/01
Posts: 160
Loc: Winter Park,Fl USA
That sounds good to me because I had the GEC attached to the water pipe and a 8 ft ground rod that I had driven

Chris
Top
#188124 - 07/22/09 11:23 AM Re: gas pipe used as grounding electrode [Re: Chris Rudolph]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Chris
One reason to bond the pipe is in case it gets hit by lightning and brings the energy into the house. Here the gas pipes in the ground are plastic but some places are metal. The gas meters usually have a dielectric fitting to isolate the interior piping from the exterior. We always want the bonding connection on the house side of the meter and the gas company wants it there too. the dielectric fitting is to control galvanic corrosion on the underground gas pipes.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 70 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals