The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 18
sparky 9
gfretwell 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 257 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#188087 - 07/21/09 08:38 AM gas pipe used as grounding electrode
Chris Rudolph Offline
Member

Registered: 05/01/01
Posts: 160
Loc: Winter Park,Fl USA
I have updated the service,150 amps,breaker panel,and installed a new grounding system in a single family house with basement in Upstate New York.The inspector said all was done well except that I had to clamp the grounding electrode conductor to the gas pipe in the basement.
Is this a violation of NEC 2002 250.52 B 1?
Chris

Top
2014 / 2011 NEC & Related Books and Study Guides
#188089 - 07/21/09 09:28 AM Re: gas pipe used as grounding electrode [Re: Chris Rudolph]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
That is not the ground electrode, it is bonding the gas pipe (250.104(B))
He also could have said you bond to the circuit EGC "likely to energize" the pipe. That will usually be the largest piece of electrical equipment connected to the gas pipe. (range electric igniter, furnace blower etc)
He might even say that was the A/C compressor via the freon line set to the A coil in the furnace. The safest alternative is the GEC, then all bases are covered.
_________________________
Greg Fretwell

Top
#188103 - 07/21/09 01:14 PM Re: gas pipe used as grounding electrode [Re: gfretwell]
Chris Rudolph Offline
Member

Registered: 05/01/01
Posts: 160
Loc: Winter Park,Fl USA
That sounds good to me because I had the GEC attached to the water pipe and a 8 ft ground rod that I had driven

Chris

Top
#188124 - 07/22/09 11:23 AM Re: gas pipe used as grounding electrode [Re: Chris Rudolph]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Chris
One reason to bond the pipe is in case it gets hit by lightning and brings the energy into the house. Here the gas pipes in the ground are plastic but some places are metal. The gas meters usually have a dielectric fitting to isolate the interior piping from the exterior. We always want the bonding connection on the house side of the meter and the gas company wants it there too. the dielectric fitting is to control galvanic corrosion on the underground gas pipes.