#187872 - 07/12/09 10:09 PM Ice machine conduit 'repair'
Bigplanz Offline
Member

Registered: 03/06/09
Posts: 72
Loc: Louisville, Kentucky
At my local CVS their ice machine is outside by the door. No GFCI on the outlet I guess (didn't test it) but what caught my eye was this 'repair' of a piece of broken PVC conduit. Doubt it is 'water tight.' smile


Attachments
IMG_0002.jpg



Top
2014 / 2011 NEC & Related Books and Study Guides
#188045 - 07/18/09 10:37 PM Re: Ice machine conduit 'repair' [Re: Bigplanz]
JoeKP Offline
Member

Registered: 03/29/08
Posts: 144
Loc: Berkley, MA
HAHA, nice, it looks kind offset, was there some kind of pull box there before the duct tape took over??
_________________________
-Joe
“then we'll glue em' then screw em'”
-Tom Silva
TOH

Top
#188075 - 07/20/09 08:31 PM Re: Ice machine conduit 'repair' [Re: JoeKP]
Bigplanz Offline
Member

Registered: 03/06/09
Posts: 72
Loc: Louisville, Kentucky
The power was from above, and there was a box that the line came out of. I reported this to property maintenance which flagged it as 'low priority.' smile

Top
#188094 - 07/21/09 11:39 AM Re: Ice machine conduit 'repair' [Re: Bigplanz]
Theelectrikid Offline
Member

Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
Looks like the CVS by Five Points, usually after they do their weekly repair of their brick wall car damage.

Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?

Top
#188110 - 07/21/09 07:53 PM Re: Ice machine conduit 'repair' [Re: Theelectrikid]
Bigplanz Offline
Member

Registered: 03/06/09
Posts: 72
Loc: Louisville, Kentucky
I think EMT or rigid would have been a better choice. Here you can see the carts and cars run straight into the PVC conduit. You can see the broken splice right above where the cart is leaning on the conduit. PVC is ok, but not in an application like this.


Top
#188111 - 07/21/09 08:44 PM Re: Ice machine conduit 'repair' [Re: Bigplanz]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
This illustrates one of the 'unenforceable' parts of the NEC.

110.3(A)(1) states that in judging an installation, 'suitavility' shall be considered. Too often, this is limited to looking for a UL lable. That's a mistake, in part because (2) goes on to address the 'adequacy' of the protection. (8), at the end of 110.3, even has a 'catch-all' provision allowing for the consideration of 'other factors.'

110.12(B) addresses the integrety of equipment, saying that there shall be no damaged parts that may affect safe operation.

The second part of the puzzle was that inspections happen only in response to a permit at the time of installation. There seems to be no provision for anyone to act afterwards - even when the failings are not only obvious, they are in a public place (and thus there is no expectation of privacy).

Were I to be asked to repair such an installation, I would consider it a requirement to take the impact of shopping carts into account with my repair. If that meant adding a guard, additional supports, or even changing the wiring method, I would do so. Simply replacing one failed system with another inadequate one does not, IMO, meet your code obligations.

Top
#188116 - 07/22/09 06:04 AM Re: Ice machine conduit 'repair' [Re: renosteinke]
Bigplanz Offline
Member

Registered: 03/06/09
Posts: 72
Loc: Louisville, Kentucky
This installation has multiple issues. The receptacle with no cover, being another. I doubt they got a permit for this. I can't see this passing an inspection.



Top
#188148 - 07/23/09 01:06 AM Re: Ice machine conduit 'repair' [Re: Bigplanz]
TOOL_5150 Offline
Member

Registered: 08/01/07
Posts: 62
Loc: Bay Area
At least they used tapcons.

~Matt
_________________________
I would rather beg for forgiveness then beg for permission.

Top
#188151 - 07/23/09 06:47 AM Re: Ice machine conduit 'repair' [Re: TOOL_5150]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Weatherproof while in use covers (bubble covers) have mixed survival rates. I would have an issue with the one in the pic, as to it's orientation,

That said, once an inspection is completed and approved, I have no 'legal' jurisdiction. The issue falls under 'property maintenance' in a lot of localities. However, situations similar to the pic result in a phone call to the uniformed fire dept inspector, as he/she can write it up as a safety item, and also write $$$ violations if it is ignored.
_________________________
John

Top
#188351 - 08/01/09 05:58 PM Re: Ice machine conduit 'repair' [Re: HotLine1]
mhulbert Offline
Member

Registered: 10/19/04
Posts: 133
Loc: Anaheim, CA USA
Re the outlet, a bubble cover would have broken just as fast as the PVC flip lid cover that they used. A better solution is to hide the plug behind the machine.

Top