The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 109 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#187735 - 07/08/09 05:35 AM Pool pump question.
petey_c Offline
Member

Registered: 01/30/05
Posts: 62
Loc: Miller Place, NY USA
Got a service call while at a supply house. Older man said that his pump (1 HP 120 VAC Hayward) had tripped his GFI and wouldn't reset. So he changed the GFI and it still tripped. Okay, I figured that he installed it incorrectly. Got to his house and it was a dedicated 15 amp circuit with the GFI wired correctly. PVC pipe from the panel, to a switch, then to the box for the GFI. Here's what transpired: changed GFI, still tripping. (Initial start current 17.5 amps (for about half a second), then settles down to 10.8). Ran temp 14/2 from panel to GFI, still trips. GFI in garage runs pump without tripping. Gremlins or...? Thanks, petey.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#187737 - 07/08/09 05:48 AM Re: Pool pump question. [Re: petey_c]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Pete,
You own a Megger?
What I would do is disconnect the motor, open the terminal box up, disconnect the C-switch and megger the Start and Run windings to Ground.
That should give you an idea of what is going on there.
It sounds to me like you have a winding down to Ground within the pump motor.

With it being a 120V motor, you should only use a 250V megger test.

Hope this is of help.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#187738 - 07/08/09 05:53 AM Re: Pool pump question. [Re: Trumpy]
petey_c Offline
Member

Registered: 01/30/05
Posts: 62
Loc: Miller Place, NY USA
Trumpy, I'll borrow a megger from my other job. This pump is only three years old. We thought it was probably going south due to all the rain we've had here this past few weeks, but when it didn't trip the other GFI... I just didn't want the customer to spend $400-500 for a new pump to have the same problem arise.

Top
#187741 - 07/08/09 08:48 AM Re: Pool pump question. [Re: petey_c]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
If it was water I would expect the problem to clear if you ran the pump for a while ... at least until it rains again.
I know the drill I use to mix mortar and grout will trip the GFCI if I get it a little wet but if I take it to a non-GFCI and run it for a minute or two the problem goes away. wink
_________________________
Greg Fretwell

Top
#187758 - 07/08/09 06:34 PM Re: Pool pump question. [Re: gfretwell]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Petey:

Hang on a sec...
You said the pump runs from another GFI in the garage??

Did you check the switch, etc wiring without the pump plugged in? And the conductors in the PVC?

Does he have a straight blade male cap on the Hayward pump? AG pool pumps are factory (Hayward) with twistlock!

The GFI is a GFI receptacle at the pump location?
_________________________
John

Top
#187776 - 07/09/09 09:09 AM Re: Pool pump question. [Re: HotLine1]
sabrown Offline
Member

Registered: 12/12/02
Posts: 297
Loc: Ogden, Utah, USA
I am sorry to ask this, as I am sure you have already thought of it, but does the GFI that the pump will run on trip using the test button on it?

Top
#187793 - 07/09/09 06:16 PM Re: Pool pump question. [Re: sabrown]
ChicoC10 Offline
Member

Registered: 05/30/07
Posts: 169
Loc: CA
Sounds like the GFI in the garage could be bad. Try running a cord to the bathroom and/or kitchen, assuming they have GFI's.

Top
#187806 - 07/10/09 06:10 AM Re: Pool pump question. [Re: ChicoC10]
petey_c Offline
Member

Registered: 01/30/05
Posts: 62
Loc: Miller Place, NY USA
This is why I thought of gremlins...: Dedicated 15 A 120 VAC ckt. to SP switch to GFI (GFI 1) near pump location. Changed customer supplied GFI (GFI 1 to my own GFI 2) - still trips. Runs okay on another (older) GFI (GFI 3) in garage on extension cord. Bypassed switch - still trips. Bypassed entire run from panel to GFI, still trips. Changed breaker (getting desperate...) - still trips. Runs okay on non-GFI receptacle (and draws 17 + amps for a half a sec or so). Ground and neutral connections good. Replaced GFI 3 with GFI 2 and it runs okay. (cue spookey music....)Thinking about going to a GFI breaker....

Top
#187817 - 07/10/09 02:43 PM Re: Pool pump question. [Re: petey_c]
FountainGuy Offline
Member

Registered: 03/15/06
Posts: 30
Loc: Lawrenceville,GA, U.S.A
Petey, I think that the 1HP pump at 115V should be on a 30A breaker, but the system might squeek by with a 20A breaker. I don't think that its a ground fault issue. The #14 wire is ok, but my Square-D motor sizing chart says that the breaker should be 30A.

Below is a link from Square D so that you can download an IEC Motor Data Calculator and other small but helpful product selection programs. Hope this helps.

http://www.schneider-electric.us/support...d-online-tools/

Top
#187820 - 07/10/09 03:39 PM Re: Pool pump question. [Re: petey_c]
Happy Birthday LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
When you tested the pump with the first and second GFI in the garage(GFI 3 & GFI 2), was the pump still connected to the pool water? Perhaps the ground leakage path is thru the pump shaft, into the pool water and to earth via the pool ...

Obvious question: Can you verify the connection between the ground pin of the pump cord plug and the pump & motor case?

Top