The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
1 registered (ampherder), 63 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#187496 - 06/28/09 08:29 PM Which Cartridge Fuse?
thiggy Offline
Member

Registered: 05/12/04
Posts: 25
Loc: B'ham Al
I have an old family farm house with a 125 amp Square D breaker box. The service disconnect is a 100 amp Square D cartridge fuse. I have never had the main blow, but I decided that I better have a spare pair of fuses on hand just in case, as in this rural area it would be difficult to locate one in a hurry. I drove to the nearest city and located fuses at Lowes, but I am not sure which one of the two types they had should be used for my application. The heavy-duty time-delay one said it is "for motor and main panel protection. (FRN-R)" It indicated that "for lighting or electric heating circuits use general purpose fuses.(NON)" I use window AC units for cooling, and 1500 watt portable heaters for infrequent use in winter heating. Water heaters are also electric. (This is generally just a week-end house.) Which type of fuse would be the most appropriate for my use?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#187497 - 06/28/09 10:41 PM Re: Which Cartridge Fuse? [Re: thiggy]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I would go with the FRN.
That will tolerate a short time spike in current.
The biggest opportunity for a spike in current is when you have a power glitch and the service would see locked rotor from every motor that was running at that time.
_________________________
Greg Fretwell

Top
#187499 - 06/29/09 01:28 AM Re: Which Cartridge Fuse? [Re: gfretwell]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8530
Loc: SI,New Zealand
Yeah,
I agree with Greg.
You really need something with a bit of time delay on it for a main fuse.
After all, the fuse/CB that is electrically closest to the fault (ie, a sub-circuit fuse/CB) should operate first, in any electrical system.
Anything less is poor design.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#187503 - 06/29/09 09:19 AM Re: Which Cartridge Fuse? [Re: Trumpy]
electure Offline

Member

Registered: 12/24/00
Posts: 4225
Loc: Fullerton, CA USA
You answered your own question.

Quote:
The heavy-duty time-delay one said it is "for motor and main panel protection. (FRN-R)"

Top
#187509 - 06/29/09 10:09 AM Re: Which Cartridge Fuse? [Re: Trumpy]
thiggy Offline
Member

Registered: 05/12/04
Posts: 25
Loc: B'ham Al
Thanks for the responses. I shall go with the time delay fuse. (I actually bought two of both types with the intention of returning one pair after I determined which type I should use.)

Top
#187517 - 06/29/09 05:24 PM Re: Which Cartridge Fuse? [Re: thiggy]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
There is almost no reason to ever install an NON fuse. For all intents NONs are old technology, and are almost always sold based on price only.

Top
#187526 - 06/29/09 08:36 PM Re: Which Cartridge Fuse? [Re: JBD]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
We used NONs to protect electronics and there was even a faster blowing fuse that we used for the input to switcher power supplies way back when they were a big cabinet full very expensive parts.
_________________________
Greg Fretwell