#187363 - 06/24/09 10:55 AM transformer help needed
jkmscottie Offline
New Member
Registered: 06/24/09
Posts: 2
Loc: ks
I am trying to get from 208v with 2 wires to 240 on 1 wire to ground any ideas on how to achieve this?
Top
Work Gear for Electricians and the Trades
#187364 - 06/24/09 11:36 AM Re: transformer help needed [Re: jkmscottie]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
_________________________
Greg Fretwell
Top
#187365 - 06/24/09 12:29 PM Re: transformer help needed [Re: gfretwell]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I just looked it up and they have 208 to 120/240 from 1 KVA to 75 KVA.
Search by keyword "208 primary" and look at the single phase units.
You don't say anything in your profile but I am assuming you know the ramifications of installing a transformer.
_________________________
Greg Fretwell
Top
#187366 - 06/24/09 02:31 PM Re: transformer help needed [Re: gfretwell]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Are you sure you want "240 on 1 wire to ground"

240 is 2 'hots', 240 volt leg to leg, and 120 volt leg to ground and/or neutral.

Your profile says that you are an electrician, is that correct??

_________________________
John
Top
#187368 - 06/24/09 04:32 PM Re: transformer help needed [Re: HotLine1]
GA76JW Offline
Member
Registered: 03/20/04
Posts: 193
Loc: Suwanee, GA USA
I'd be interested to hear what application you are using this for?????

I can't say as I have heard of anything that uses 240 on one leg yet.
_________________________
"If common sense was common, everyone would have it"-not sure, someone here

Top
#187369 - 06/24/09 04:40 PM Re: transformer help needed [Re: GA76JW]
jkmscottie Offline
New Member
Registered: 06/24/09
Posts: 2
Loc: ks
Yes i am an electricain. I am working on a heater project for the company i am working for now. It is for leakage current testing on heaters. They specified and asked if i can get. I am told that an isolation transformer will do the job. Staco said they can do it. Just checking with you all to see what your opinions are on this.
Thank You
Top
#187373 - 06/24/09 07:05 PM Re: transformer help needed [Re: jkmscottie]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The transformers you get with a "208 primary" search (second pane down) are right up your alley. For test equipment you could even switch the output topology to test with 3 different grounding references.
_________________________
Greg Fretwell
Top
#187374 - 06/24/09 07:24 PM Re: transformer help needed [Re: gfretwell]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
Why not a megger?
Top
#187376 - 06/24/09 07:29 PM Re: transformer help needed [Re: twh]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
WAG? Testing under normal load conditions?

BTW, you can get this at Grainger but you will save about 40% if you have your supply house order you one.

BTDT

Better feed the little guy anyway.
_________________________
Greg Fretwell
Top
#187476 - 06/27/09 07:30 PM Re: transformer help needed [Re: gfretwell]
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
jkmscottie

Welcome to ECN.

Obtain a "Standard", off-the-shelf Single Phase Isolated Transformer, which has a 208V Primary, and 240V Secondary.

Feed the Transformer with a normal 208V 1 Phase 2 Wire + EGC (Equipment Grounding Conductor) Circuit.

On the Secondary side, ground either one of the "X" Terminal outputs... for example, Ground "X2".

Now you have a 240V 2 Wire system with an Ungrounded Conductor and a Grounded Conductor.

The correct way to describe your desired 240V Circuit is:

240V 1 Phase 2 Wire Grounded Circuit.

One "Side" of the Circuit is Ungrounded ("Hot" to Ground),
The other "Side" of the Circuit is Grounded - just like the "Neutral" on a 1 Phase 3 Wire Circuit, or the Common "Neutral" on a 208Y/120V 3 Phase 4 Wire Circuit.

Match the KVA rating to the KVA requirement for the test loads. Since the test loads are Resistance type loads, the power ratings will (almost always) be in KW (Kilo Watts).
If the Heaters consist of only Heater Elements, then the KW ratings will equal KVA.

If these loads only have Ampere ratings, multiply the Amperes by 240, which will show the KW / KVA rating.
example:
Heater Element listed for 240V, FLA = 10
240 x 10 = 2400 VA (Volt-Amps)
Minimum KVA requirement: 2.4 KVA
Transformer size: 3.0 KVA

Good luck.

Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals