The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 18
sparky 9
gfretwell 9
sparky66wv 8
Vlado 6
Who's Online
2 registered (cableguy619, mbhydro), 230 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#186585 - 05/20/09 04:06 AM how to size wire for voltage drop
lite bulb Offline
Member

Registered: 02/12/06
Posts: 77
Loc: wilm,de.
I need to feed a 200 amp 3ph 120/240 panel from the power co. 450' will be (al) areial and 110' will be (cu)underground over to the panel. How do you size the wire for voltage drop

Top
2014 / 2011 NEC & Related Books and Study Guides
#186587 - 05/20/09 05:39 AM Re: how to size wire for voltage drop [Re: lite bulb]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Compute the two separately, and add up the cumulative voltage drop. You can use the tables in the back of NEC, or one of the calculators online like this one: http://www.csgnetwork.com/voltagedropcalc.html

Do you mean 3-phase 120/208, or 1-phase 120/240?

FYI, the "half-length" the calculations ask for, in your case, would be 450' and 110', as the electricity has to take a return trip down back the same wire, so the actual electrical length required for calculating voltage drop would be twice that.

Top
#186588 - 05/20/09 05:46 AM Re: how to size wire for voltage drop [Re: lite bulb]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
We need more information to calculate the wire size. Namely what is the expected load on the panel. It would not be practical to size the wire for a 200a. load and try to maintain the 240/120v. status. Once we know the "load" we need to know what voltage drop you can tolerate. Then there are formulae for giving you the wire size.
_________________________
George Little

Top
#186589 - 05/20/09 05:47 AM Re: how to size wire for voltage drop [Re: SteveFehr]
sparky Offline
Member

Registered: 10/18/00
Posts: 5542
don't most poco's do the sizing inclusive in their doctrine for us?

~S~

Top
#186590 - 05/20/09 06:36 AM Re: how to size wire for voltage drop [Re: sparky]
lite bulb Offline
Member

Registered: 02/12/06
Posts: 77
Loc: wilm,de.
The service is 120/240 3ph hi leg and the connected load is 150 amp. motor load.

Top
#186598 - 05/20/09 10:29 AM Re: how to size wire for voltage drop [Re: lite bulb]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Oh wow, there's going to be some SERIOUS kick-down when that motor starts. What's the locked-rotor current for that motor?

This is a textbook case where you're probably better off stepping up to a higher voltage and stepping back down. Any chance of getting your service at 480V and using a 480V motor? This will eliminate the need for two 72kVA transformers. You can throw on a small transformer for the 120V loads, and come out WAY ahead in copper.

Top
#186602 - 05/20/09 04:25 PM Re: how to size wire for voltage drop [Re: SteveFehr]
lite bulb Offline
Member

Registered: 02/12/06
Posts: 77
Loc: wilm,de.
I have three 7-1/2 hp one 5 hp thats 108 amps with the 125%, the 42 amps is lighting. I should have listed it earlier in the post it looks like there is 150 amps in motor load but there is not.


Edited by lite bulb (05/20/09 04:30 PM)

Top
#186608 - 05/20/09 06:18 PM Re: how to size wire for voltage drop [Re: lite bulb]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I agree with Steve. Consider also getting a separate drop from the utility company. Getting that much power over that distance is extremely expensive. Get an engineer to figure your wire size if you can't get the utility to give you a separate drop. I could figure it out but I think you'd end up with xformers as the best route if the utility can't accommodate you with a drop.
_________________________
George Little

Top
#186612 - 05/20/09 08:33 PM Re: how to size wire for voltage drop [Re: George Little]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Litebulb:

Is your question in this thread a 'school project'?
_________________________
John

Top
#186622 - 05/21/09 12:12 PM Re: how to size wire for voltage drop [Re: HotLine1]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Ya know John, I think you are right, I seem to remember that same problem showing up before and it was off some test or school project someplace. I'm sticking with my suggestion and see what happens smile
_________________________