The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Temporarily feeding a panel...
by renosteinke
09/29/16 05:10 PM
Locked rotor, no burnout
by jraef
09/29/16 01:18 PM
Massive power outage South Australia
by Meadow
09/29/16 06:46 AM
short circuit??
by Meadow
09/29/16 06:43 AM
Norwegian power?
by Meadow
09/29/16 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
sparky66wv 8
gfretwell 8
Potseal 6
Who's Online
1 registered (mbhydro), 296 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#186569 - 05/19/09 12:23 PM 25 KVA Transformer grounding
wewire2 Offline
Member

Registered: 11/14/02
Posts: 246
Loc: California
Would it be OK to run the grounding electrode conductor for a 25 KVA 3 phase 480-208Y/120V transformer to the existing service ground in the adjacent switchgear? The only accessible building steel is bolted together lattice trusses(not a reliable ground)and the water entrance piping is not in the vicinity? Driving a ground rod would be extremely risky due to existing unknown substructures.

Top
2014 / 2011 NEC & Related Books and Study Guides
#186577 - 05/19/09 06:14 PM Re: 25 KVA Transformer grounding [Re: wewire2]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
I'd say read 250.30 A(7)
Exception # 2.
2005 N.E.C.

Top
#186584 - 05/19/09 11:57 PM Re: 25 KVA Transformer grounding [Re: Yoopersup]
wewire2 Offline
Member

Registered: 11/14/02
Posts: 246
Loc: California
Good advice,thank you. I skipped right over that exception in my quest for the answer. The transformer is fed from a subpanel that is fed from the switchgear. I guess the next step is to verify whether the subpanel is suitable for use as service equipment.
Now I'm wondering what criteria the manufacturer must abide by in having their product listed as suitable for use as service equipment.

Top