Is an expansion fitting needed when a 4 inch s80 PVC is stubbed out of the ground to the bottom of a 400 amp disconnect switch (3R)?
Top
Work Gear for Electricians and the Trades
#186338 - 05/06/09 02:23 AM Re: PVC underground installation [Re: sparky13090]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
nope. Expansion fittings are only required in exposed areas like on roofs or exterior overhead racks.


Edited by sparkyinak (05/06/09 02:24 AM)
_________________________
"Live Awesome!" - Kevin Carosa
Top
#186341 - 05/06/09 07:33 AM Re: PVC underground installation [Re: sparkyinak]
homer Offline
Member
Registered: 09/30/04
Posts: 68
Loc: Vancouver, WA, USA
Sparkyinak is technically correct according to NEC 352.44. There is not enough thermal expansion in the 7' of PVC riser to need an expansion fitting.

However, frost heave can cause damage to PVC. As the ground freezes in areas of cold winters, the ground actually slowly rises. This can put quite a bit of pressure on a PVC riser if it is entering a CT cabinet or other fixed cabinet. PVC also gets very brittle when cold and also as it ages. So over time, pvc conduits in cold areas can be damaged by the frost.

I have been asked to install expansion fittings by inspectors in cold areas, and some inspectors interpret 352.44 to include frost heave movement, even though it is not specifically mentioned. This subject certainly can be debated either way, depending on your point of view.
Top
#186342 - 05/06/09 08:06 AM Re: PVC underground installation [Re: homer]
leland Offline
Member
Registered: 08/20/07
Posts: 853
Loc: Lowell area, Ma. USA
352.40 "......shall be fastened so that movement from thermal expansion or contraction shall be permitted."

352.44 calls for expansion fitting if movement of 1/4" or more is expected."In a straight run between securely mounted items...." (2008 NEC)

My direct answer (opinion)Would be: if you anticipate a 1/4" movement or more, Yes, you need an expansion fitting.
Top
#186351 - 05/06/09 09:42 PM Re: PVC underground installation [Re: leland]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Although the NEC does not spell it out, the NEC handbooks states that expansion fittings are not typically used in underground work. typically pipes are buried below the frost line to prevent upheaval (spelling). Below the frot line the temp is pretty much constant. I also do believe if you read the expansion fittings lititerture, it also talks about not needed in underground work
_________________________
"Live Awesome!" - Kevin Carosa
Top
#186352 - 05/06/09 10:24 PM Re: PVC underground installation [Re: sparkyinak]
leland Offline
Member
Registered: 08/20/07
Posts: 853
Loc: Lowell area, Ma. USA
Agreed Sparky. (never intended to imply expansions under ground)
By the way,I have never seen the conduit move and the wires not.
So when does the 'expansion Conductors' come out? smile

the system worked this long,Why the change? (rhetorical of course)
Top
#186359 - 05/07/09 11:00 AM Re: PVC underground installation [Re: leland]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Aren't concentric knockouts "expansion fittings"? wink
That is usually what I see separate if the PVC moves.

The wire usually has enough slack that it can take up any movement in the raceway.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals