The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#186334 - 05/05/09 08:13 PM PVC underground installation
sparky13090 Offline
New Member

Registered: 10/20/04
Posts: 1
Loc: Syracuse, ny usa
Is an expansion fitting needed when a 4 inch s80 PVC is stubbed out of the ground to the bottom of a 400 amp disconnect switch (3R)?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#186338 - 05/06/09 02:23 AM Re: PVC underground installation [Re: sparky13090]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1295
Loc: Alaska
nope. Expansion fittings are only required in exposed areas like on roofs or exterior overhead racks.


Edited by sparkyinak (05/06/09 02:24 AM)
_________________________
"Live Awesome!" - Kevin Carosa

Top
#186341 - 05/06/09 07:33 AM Re: PVC underground installation [Re: sparkyinak]
homer Offline
Member

Registered: 09/30/04
Posts: 68
Loc: Vancouver, WA, USA
Sparkyinak is technically correct according to NEC 352.44. There is not enough thermal expansion in the 7' of PVC riser to need an expansion fitting.

However, frost heave can cause damage to PVC. As the ground freezes in areas of cold winters, the ground actually slowly rises. This can put quite a bit of pressure on a PVC riser if it is entering a CT cabinet or other fixed cabinet. PVC also gets very brittle when cold and also as it ages. So over time, pvc conduits in cold areas can be damaged by the frost.

I have been asked to install expansion fittings by inspectors in cold areas, and some inspectors interpret 352.44 to include frost heave movement, even though it is not specifically mentioned. This subject certainly can be debated either way, depending on your point of view.

Top
#186342 - 05/06/09 08:06 AM Re: PVC underground installation [Re: homer]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
352.40 "......shall be fastened so that movement from thermal expansion or contraction shall be permitted."

352.44 calls for expansion fitting if movement of 1/4" or more is expected."In a straight run between securely mounted items...." (2008 NEC)

My direct answer (opinion)Would be: if you anticipate a 1/4" movement or more, Yes, you need an expansion fitting.

Top
#186351 - 05/06/09 09:42 PM Re: PVC underground installation [Re: leland]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1295
Loc: Alaska
Although the NEC does not spell it out, the NEC handbooks states that expansion fittings are not typically used in underground work. typically pipes are buried below the frost line to prevent upheaval (spelling). Below the frot line the temp is pretty much constant. I also do believe if you read the expansion fittings lititerture, it also talks about not needed in underground work
_________________________
"Live Awesome!" - Kevin Carosa

Top
#186352 - 05/06/09 10:24 PM Re: PVC underground installation [Re: sparkyinak]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Agreed Sparky. (never intended to imply expansions under ground)
By the way,I have never seen the conduit move and the wires not.
So when does the 'expansion Conductors' come out? smile

the system worked this long,Why the change? (rhetorical of course)

Top
#186359 - 05/07/09 11:00 AM Re: PVC underground installation [Re: leland]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Aren't concentric knockouts "expansion fittings"? wink
That is usually what I see separate if the PVC moves.

The wire usually has enough slack that it can take up any movement in the raceway.
_________________________
Greg Fretwell

Top