#186147 - 04/21/09 10:18 PM High Leg
NORCAL Offline
Member
Registered: 09/25/02
Posts: 865
Section 408.3 (E) (2005) requires the high leg of a 3 4-wire delta system to the B phase, would there be a requirement to also locate same phase to the B phase in a safety switch, or motor starter other then keeping things the same/consistent everywhere?
Top
2017 / 2014 NEC & Related Books and Study Guides
#186148 - 04/21/09 10:30 PM Re: High Leg [Re: NORCAL]
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
Rollie .,

Typically with most Delta system the B phase or wild leg useally are landed on centre lugs in most place unless marked otherwise and if you have 4 wire system then yes you also have to mark the conductor with correct colour useally orange { I know few spots will ask for purple colour }

If you run into old Delta system it will useally marked in red so watch out on that one.

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#186151 - 04/22/09 12:49 AM Re: High Leg [Re: frenchelectrican]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Marking the high leg orange has been in the code for over 20 years.
_________________________
Greg Fretwell
Top
#186153 - 04/22/09 07:07 AM Re: High Leg [Re: gfretwell]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
The Code reference given applies to panelboards and switchboards only.....

Do the same rules apply to motor starters and safety switches?

(not the orange tape, or in the case of San Francisco violet tape)

Top
#186154 - 04/22/09 08:09 AM Re: High Leg [Re: electure]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Says Orange or marked & only required when a Neutral is present.
Top
#186157 - 04/22/09 10:45 AM Re: High Leg [Re: Yoopersup]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
If there is no neutral present it is not particularly important which is the B phase since they are all ungrounded conductors and should be treated with the same respect. The only regard in line to line loads is phase rotation but you still need unique marking to identify the system they are connected to.
We do have in inconsistency between the code and industry practice. The code says the B phase of a center delta shall be orange but orange is also commonly used on 480 wye "BOY".
_________________________
Greg Fretwell
Top
#186174 - 04/23/09 06:36 PM Re: High Leg [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Utility (PSE&G) requires high leg within their equipment to be on 'C' phase.....and marked orange. They do not allow 'boy' on 277/480 volt in their equipment. Orange only on a high leg system.

Any other POCOs specs like this??
_________________________
John
Top
#186176 - 04/23/09 09:48 PM Re: High Leg [Re: HotLine1]
wire twister Offline
Member
Registered: 11/25/06
Posts: 23
Loc: Washington GA USA
Around here, Georgia all the pocos want the high leg on the c phase in their meters and marked with orange tape. As far as I know there is no problem using BOY on 277/480 systems.
Top
#186181 - 04/24/09 06:19 PM Re: High Leg [Re: wire twister]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Nec deals with Utility Co. High leg on C phase :
408.3 (E) Exception.
Yoopers
Most Utility Companys require the High leg on C phase in there metering Equipment.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 30 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals