Correct rotation, wrong sequence
by Potseal
Yesterday at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
1 registered (geoff in UK), 205 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#186147 - 04/21/09 10:18 PM High Leg
NORCAL Offline
Member

Registered: 09/25/02
Posts: 807
Section 408.3 (E) (2005) requires the high leg of a 3 4-wire delta system to the B phase, would there be a requirement to also locate same phase to the B phase in a safety switch, or motor starter other then keeping things the same/consistent everywhere?

Top
2014 / 2011 NEC & Related Books and Study Guides
#186148 - 04/21/09 10:30 PM Re: High Leg [Re: NORCAL]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
Rollie .,

Typically with most Delta system the B phase or wild leg useally are landed on centre lugs in most place unless marked otherwise and if you have 4 wire system then yes you also have to mark the conductor with correct colour useally orange { I know few spots will ask for purple colour }

If you run into old Delta system it will useally marked in red so watch out on that one.

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#186151 - 04/22/09 12:49 AM Re: High Leg [Re: frenchelectrican]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Marking the high leg orange has been in the code for over 20 years.
_________________________
Greg Fretwell

Top
#186153 - 04/22/09 07:07 AM Re: High Leg [Re: gfretwell]
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
The Code reference given applies to panelboards and switchboards only.....

Do the same rules apply to motor starters and safety switches?

(not the orange tape, or in the case of San Francisco violet tape)


Top
#186154 - 04/22/09 08:09 AM Re: High Leg [Re: electure]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Says Orange or marked & only required when a Neutral is present.

Top
#186157 - 04/22/09 10:45 AM Re: High Leg [Re: Yoopersup]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
If there is no neutral present it is not particularly important which is the B phase since they are all ungrounded conductors and should be treated with the same respect. The only regard in line to line loads is phase rotation but you still need unique marking to identify the system they are connected to.
We do have in inconsistency between the code and industry practice. The code says the B phase of a center delta shall be orange but orange is also commonly used on 480 wye "BOY".
_________________________
Greg Fretwell

Top
#186174 - 04/23/09 06:36 PM Re: High Leg [Re: gfretwell]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
Utility (PSE&G) requires high leg within their equipment to be on 'C' phase.....and marked orange. They do not allow 'boy' on 277/480 volt in their equipment. Orange only on a high leg system.

Any other POCOs specs like this??
_________________________
John

Top
#186176 - 04/23/09 09:48 PM Re: High Leg [Re: HotLine1]
wire twister Offline
Member

Registered: 11/25/06
Posts: 23
Loc: Washington GA USA
Around here, Georgia all the pocos want the high leg on the c phase in their meters and marked with orange tape. As far as I know there is no problem using BOY on 277/480 systems.

Top
#186181 - 04/24/09 06:19 PM Re: High Leg [Re: wire twister]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Nec deals with Utility Co. High leg on C phase :
408.3 (E) Exception.
Yoopers
Most Utility Companys require the High leg on C phase in there metering Equipment.

Top