#186068 - 04/14/09 07:19 PM Hospital Grade Receptacles your comments
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Hospital Grade Receptacles required per Nec in Patient Bed Locations/.
Exam rooms at Doctors offices are NOT Patient Bed Locations.
Exam tables Doctors offices come with Hospital Grade Plugs feeding Hospital Grade Outlets on theses Exam tables.

Code then as I see says Hosptal Grade Outlets NOT required.
BUT Listing & Lableing of Exam table does.
Interesting . Yoopersup

Top
2017 / 2014 NEC & Related Books and Study Guides
#186070 - 04/14/09 07:48 PM Re: Hospital Grade Receptacles your comments [Re: Yoopersup]
luckyshadow Offline
Member
Registered: 01/04/05
Posts: 305
Loc: Maryland USA
Yep thats about the way it is.
Watch out for those dental chairs also. I've been seeing ones that have a tag on them that require they be plugged into a Hospital Grade Receptacle
Top
#186083 - 04/15/09 06:58 AM Re: Hospital Grade Receptacles your comments [Re: luckyshadow]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Equip mfg specs on most (if not all) medical equipment I have seen require HG receptacles to match the HG cord cap.

Most EC's here just put them in as SOP. Our hospital stocks ALL HG devices, so there can be no 'mistakes'.

_________________________
John
Top
#186088 - 04/15/09 03:22 PM Re: Hospital Grade Receptacles your comments [Re: HotLine1]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Yep I agree with the need for Hospital Grade receptacles in these areas where the equipment is equipped with Hospital Grade caps. I think it should also be mentioned that the redundant ground conductor is required whether or not the receptacle is Hospital Grade or not. Of course we all knew that, but it's the weasel in me that had to say it smile
_________________________
George Little
Top
#186093 - 04/15/09 08:50 PM Re: Hospital Grade Receptacles your comments [Re: HotLine1]
leland Offline
Member
Registered: 08/20/07
Posts: 853
Loc: Lowell area, Ma. USA
Originally Posted By HotLine1
Equip mfg specs on most (if not all) medical equipment I have seen require HG receptacles to match the HG cord cap.

Most EC's here just put them in as SOP. Our hospital stocks ALL HG devices, so there can be no 'mistakes'.



But... Is the wiring all HG? Thats the question.
An HG recep not wired properly can be trouble.
Top
#186094 - 04/16/09 06:21 AM Re: Hospital Grade Receptacles your comments [Re: leland]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Le:
Yes, HCF is installed. It's checked on Plan Review & field checked on inspections.

George:
Come on now!....I once had a guy spray paint BX green..LOL
_________________________
John
Top
#186099 - 04/16/09 01:20 PM Re: Hospital Grade Receptacles your comments [Re: HotLine1]
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
I have a question along the same lines, but somewhat unrelated: It used to be that phone jacks in patient rooms where oxygen was in use were required to be wired for the RJ17C standard. Does anybody know if that still applies?
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#186114 - 04/17/09 11:54 AM Re: Hospital Grade Receptacles your comments [Re: EV607797]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
In Canada a Doctors exam room, a dentists chair and even a psychiatrists couch are patient care locations. (I know it is a bit of overkill) and have to be wired as for patient care for any device located within 5 feet (1.5M) of the bed. Hospital grade receptacles and equipotential wiring are all required.
Top
#186119 - 04/18/09 12:40 PM Re: Hospital Grade Receptacles your comments [Re: mikesh]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Part VI 517.80
Try that for a start.
Top
#186132 - 04/21/09 12:15 AM Re: Hospital Grade Receptacles your comments [Re: Yoopersup]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Ernie- You just caught my attention about the communications wiring in Hospitals. In the State of Michigan you do not need a license or any training to install communication wiring in buildings. To make matters worse, you are exempt from permits and inspections. Now that will give you a warm fuzzy feeling next time your in the OR. I can't believe the telecommunication people and the lobbyist were able to pull that off but they did.
_________________________
George Little
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 80 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals