#18599 - 12/11/02 04:29 PM Laundry Circuit
master44 Offline
Member
Registered: 12/01/02
Posts: 13
Loc: Clay Center, Kansas USA
How do you interput 210.11 c (2) It says that the laundry circuit can only supply the laundry receptacle (S). But then it it says . This circuit shall have no other outlets. I was under the opinion that there could be one other recpetacle for an iron ect. It seems to me to be contradict itslf in the same paragraph. Let me know what you do in your area. Thanks Guys and of course you gals too.
Top
Work Gear for Electricians and the Trades
#18600 - 12/11/02 04:40 PM Re: Laundry Circuit
spyder Offline
Member
Registered: 10/14/02
Posts: 210
Loc: Massachusetts
It means you can't pick up lighting, recptacles in another room off this 20 amp branch circuit. The circuit can only be used for the laundry.
Top
#18601 - 12/11/02 04:42 PM Re: Laundry Circuit
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
I believe the intent of the rule is that the laundry cicuit shall supply no other outlets outside of the laundry room or area.
_________________________
Peter
Top
#18602 - 12/11/02 04:46 PM Re: Laundry Circuit
master44 Offline
Member
Registered: 12/01/02
Posts: 13
Loc: Clay Center, Kansas USA
What if they were going to set up an ironing board in close proximity to the laundry closet but was not in the closet but around the corner in the other room. Would it be ok to have this receptacle on the laundry circuit.
Top
#18603 - 12/11/02 05:16 PM Re: Laundry Circuit
spyder Offline
Member
Registered: 10/14/02
Posts: 210
Loc: Massachusetts
master 44,

I would say no.
Top
#18604 - 12/11/02 05:43 PM Re: Laundry Circuit
The Watt Doctor Offline
Member
Registered: 12/23/01
Posts: 435
Loc: Mont Belvieu, TX
210.11 (C)(2) says....shall be provided to supply the bathroom receptacle outlet(s) required by 210.52(F)....

The subtitle of 210.52 (F) is Laundry Areas

As CTwireman said
Quote:
or area


If I was the AHJ I would allow it, but that's just me. master44, give the AHJ a call, and tell them the circumstances, and if they give you a hard time ask them to "waive" it. Remember 90.4 Enforcement.

Waiving Good-Bye, and good luck,
Doc
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX
Top
#18605 - 12/12/02 01:41 AM Re: Laundry Circuit
lwinter31 Offline
Member
Registered: 11/23/02
Posts: 40
Loc: Texas
I believe it is the code panel's intention to make plural the application of 210.11 c (2) to all [210.52 (F) laundry area(s)] not the "receptacle outlet" that is sigular in (F)
Futhermore a typical washer is rated @ 10a, a typicle iron @1200va. I think a washer running and ironing clothes is a common occurence. This will skim the teeth of "noncontinuous - equal to" of 210.19 (a)

I always dedicate the laundry "washer" receptacle outlet.
Top
#18606 - 12/12/02 07:41 AM Re: Laundry Circuit
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
I would agree. That is to run the washer by it's self. It's possible that the owner may get
a gas dryer. Also that could be plugged into the same ckt. I would set up 2 single outlets for that with 1-20 amp. circuit. The iron and washer going together may trip the breaker. Why take a chance?
Top
#18607 - 12/13/02 04:28 PM Re: Laundry Circuit
GEC-1 Offline
Member
Registered: 06/06/01
Posts: 32
Loc: Covington, Georgia USA
If I was wiring this, I would pull 12/3 to the laundry room. One hot for the washer, and one hot for the iron. If you put the two circuits on different phases, the two can share the neutral. ( the neutral has to be rated to carry the difference of the unbalanced load) Now you have one wire pulled for the two applications. It's also a good way to reduce the number of homeruns you pull in a house.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 59 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals