The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
1 registered (Webmaster), 0 Guests and 69 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#185665 - 03/23/09 06:22 PM Wire for 600A 1Phase service
Obsaleet Offline
Member

Registered: 04/05/03
Posts: 361
Loc: Pa
Hi Guys, I am doing a 600a 1phase service and I was going to use 350kmcm in parallel, my friend from a diffrent firm is telling me they used 300kmcm for one just recently. Now I am second guessing myself, so I am turning to you all.


Ob
_________________________
Choose your customers, don't let them choose you.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#185667 - 03/23/09 07:08 PM Re: Wire for 600A 1Phase service [Re: Obsaleet]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6829
Loc: Brick, NJ USA
300KCMil Copper, 75 degree col is 285 amps,Based on 240.4 (B)parallel is 570 amps, next higher available is 600 amps.

300's work.
_________________________
John

Top
#185668 - 03/23/09 07:14 PM Re: Wire for 600A 1Phase service [Re: Obsaleet]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
If in two seperate conduits 300 kcmil is good for 285 amps at 75c. see 240.4 (b) (800 amps or less next higest breaker size) .
240.6 300 next breaker size is 600.
285 plus 285 = 570
if in one single conduit see table 310.15(B)(2)(a)
4-6 80%
570x80%=456 next higest per 240.6= 500amp.
Same Conduit would require 400 Kcmil
335x2= 670 x 80%= 536 . 240.6 next higest 600
This is with 3 wires in conduit single phase. Or
6 wires in conduit single phase.

Top