The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#185314 - 03/09/09 12:59 PM Wiring contactors instead of shunt trip breakers
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
I've went in the "search" menu and found some great information on "shunt trip breakers". I have a job where I will not be able to add any shunt trip breakers because the panel is packed and I know a shunt trip breaker requires another space, so I'm thinking about going just above the panel and setting a traugh and installing contactors inside the traugh to control the other circuits that need to go off when the Ansul system calls for it. Since the shunt trip breakers require 120 volts to activate it, will I not have to run another wire to the NC contact on the ansul system to energize the coils on my contactors, so that when the ansul system is activated, the coils will "drop out" on the circuits I have installed the contactors on? I was originally thinking I could come off the same wire that the other "shunt breakers" were on, but if they need the presence of 120 volts to trip, then I need the absence of 120 volts to make my contactors drop out. Thanks for the help. Steve...

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#185316 - 03/09/09 02:44 PM Re: Wiring contactors instead of shunt trip breakers [Re: sparkync]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Shunts need the voltage to open.Use a mechanical contactor N/C (like a lighting contactor).Or go back to the distribution panel and add a Main ST breaker.

Remember, what ever you use it MUST need to be manually reset.

NFPA 17A
4.4.3.7: Shut off devices shall require manual resetting prior to fuel or power being restored.

Top
#185319 - 03/09/09 06:04 PM Re: Wiring contactors instead of shunt trip breakers [Re: leland]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Lee, I think you are misreading the NFPA 17A and 95 requirements.

Either a contactor or a shunt trip breaker will be "manually reset" when the release mechanism is reset. That's just fine.

What is NOT allowed is for that resetting operation to also open up gas flow to the appliances - unless those appliances also have electric automatic spark igniters. The manual reset provision is there to help ensure that the (presumably still 'on') appliances don't fill the kitchen with gas fumes.

Since most Ansul systems use a mechanical gas valve, rather than an solenoid operated one, this is usually not an issue.

Top
#185322 - 03/09/09 07:47 PM Re: Wiring contactors instead of shunt trip breakers [Re: renosteinke]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Reno_ "Since most"-

Not all.

This I will concede as interpretation.

Perhaps I read too deep.
However,A shunt trip IS a shut off device.

lets assume (I know we should not) All appliances are electric.

Being affiliated in the industry,I will not and do not reset anything aside from 'My' equipment. If I reset and move along,Now the gas stove or electric stove (insert appliance here) Is re energized after my system is reset,Not recharged.
A new or current hazard re emerges.

Not all kitchen fires stem from a cooking situation.

Top
#186194 - 04/25/09 08:17 PM Re: Wiring contactors instead of shunt trip breakers [Re: renosteinke]
fireguy Offline
Member

Registered: 02/02/06
Posts: 19
Loc: Baker City, OR 97814
Originally Posted By: renosteinke
Lee, I think you are misreading the NFPA 17A and 95 requirements.

Either a contactor or a shunt trip breaker will be "manually reset" when the release mechanism is reset. That's just fine.

What is NOT allowed is for that resetting operation to also open up gas flow to the appliances - unless those appliances also have electric automatic spark igniters. The manual reset provision is there to help ensure that the (presumably still 'on') appliances don't fill the kitchen with gas fumes.

Since most Ansul systems use a mechanical gas valve, rather than an solenoid operated one, this is usually not an issue.


NFPA 17 and 17A require a reset relay if the gas valve is electrical. As do the manufacturers, Ansul, Amerex and Badger. Even if the appliances to have electric spark igniters, they could always be replaced later with standing pilot appliances.

Top
#186195 - 04/25/09 08:31 PM Re: Wiring contactors instead of shunt trip breakers [Re: fireguy]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I agree as to resetting the gas valve, if the gas valve is electric. Now, I cannot speak for the entire world ... but in my experience, electric valves are few and far between.

Absent such a valve, there is no need for anything special - it all - gas and power - gets reset when the trigger mechanism is reset. That's all you need.

As for the difference in resetting a shunt trip vs. resetting a contactor .... it is true that a shunt trip will require a second step to restore power. Not only must the trigger mechanism be reset, the breaker must also be reset. Which method you use is purely a design choice; I can point to situations that favor each.


Edited by renosteinke (04/25/09 08:35 PM)

Top
#186201 - 04/26/09 10:09 PM Re: Wiring contactors instead of shunt trip breakers [Re: renosteinke]
Kevink1955 Offline
New Member

Registered: 04/26/09
Posts: 2
Loc: Long Island NY
As I read the original post you already have some shunt trip breakers in the panel, I am assuming they are on the same system you need to ad the contactors to.

Why not power the contactor coils off the existing load side of the shunt trip breaker. The Ansul trips the shunt trip and the shunt trip drops the contactor for the other loads.

Top
#186231 - 04/27/09 08:26 PM Re: Wiring contactors instead of shunt trip breakers [Re: Kevink1955]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
A master shut trip that controls a slew of contactors is the way it's done for all of the Safeways I've built.

Field engineering our own schemes was never permitted.