The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#184929 - 02/25/09 06:26 PM 277Volt single phase Motors
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Why isn't there an Amperage chart on theses motors in the code book???
430.248 just goes up to 230 volts???

Top
2014 / 2011 NEC & Related Books and Study Guides
#184931 - 02/25/09 06:39 PM Re: 277Volt single phase Motors [Re: Yoopersup]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Personally,I have never seen a 277V motor.
So I never gave it a thought.

Top
#184932 - 02/25/09 06:48 PM Re: 277Volt single phase Motors [Re: leland]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Ditto on Leland's comment.

You could always refer to the motor nameplate, right?
_________________________
John

Top
#184934 - 02/25/09 07:02 PM Re: 277Volt single phase Motors [Re: HotLine1]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Per 430.6 (A)1 all amperages except for overloads & few exceptions are to come out of tables in Code book.
Since no Table with 277V I guess well have to use Nameplate for all calculations??
And yep theres 277Volt Motors Goggle um there there. These are on a Heat Pump System.

Top
#184936 - 02/25/09 07:09 PM Re: 277Volt single phase Motors [Re: Yoopersup]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
I've seen those and other type units. Also in them was a transformer to step down.

Google was the first thing I did. Always nice to find something new.

Top
#184937 - 02/25/09 07:14 PM Re: 277Volt single phase Motors [Re: leland]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Been in the trade almost 45 years have Never before this time ever Seen or Knew there were 277 volt mtrs. Guess never to late to learn right.

Top
#184939 - 02/25/09 07:25 PM Re: 277Volt single phase Motors [Re: Yoopersup]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
It's never to late, & we're never to old to learn. We come here to do that, right???

Yes, as there is no table to use, go to 110.3 (B) and use the nameplate.
_________________________
John

Top
#184940 - 02/25/09 07:26 PM Re: 277Volt single phase Motors [Re: Yoopersup]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
There is not a large number of 277 volt motour in use however most common found in HVAC or large electric unit heater AKA electric Renzor heater.

Once a while will find them on the exhaust fan when they are tied to bathroom lighting circuit { this is a grey spot to cross }

The other common place to find 277 volt motor is thru wall heatpump when they are order on 277 volt system.

Merci,Marc